Alright, I replaced the hot water tank of my Attwood pilot light gas water heater (6gal). With the tank they sent a new relief valve so I used it instead of reusing the old one. This weekend we tried it out and this morning I noticed a steady but small drip from the relief valve, my wife had just taken a shower and the burner was on. This never happened with the old one.

Is it a bad valve? Should I tighten something up (leak was not from around threads but out relief hole)?

On a side note, I got in a pinch and removed the bypass valve and connections - but that shouldn't make a difference right?

Thanks in advance,
Josh


03 Ram 1500 Quad Cab with Hemi 5.7, HD tow package, K&N Cold Air, B&W Companion + Ball, Prodigy,
1987 Prowler 27.5',
Macbook Pro 17" (Fastest Vista Laptop , iPhone)

Me and the DW and our
2 Dogs: Jackson (golden), Pumba (min-pin)


rick_niagara

Niagara Falls, Ontario, Canada

Full Member

Joined: 02/16/2008

View Profile

Offline
Posted: 06/01/08 05:49pm Link  |  Quote  |  Print  |  Notify Moderator

Give it the summer and maybe it'll seal up with hard water conditions, wont' hurt to wait and see!


2008 Fleetwood Prowler 235RLS
2005 Dodge Ram 2500 4x2 5.9L Diesel 3.73Limited slip 6speed manual
Pullin' 5ers since 1988....Have a nice day


frankandvicki

Niwot,CO

Senior Member

Joined: 05/31/2007

View Profile

Offline
Posted: 06/01/08 05:57pm Link  |  Quote  |  Print  |  Notify Moderator

Turn the input source off and flip the valve a couple of times. Probably not seated quite right.
Frank O.


Frank and Vicki
Niwot, CO
2006 Itasca Sunrise 35A

States visited/camped in, not just driven through.


Polishnurse

Schodack, NY

Senior Member

Joined: 03/13/2007

View Profile

Offline
Posted: 06/01/08 05:58pm Link  |  Quote  |  Print  |  Notify Moderator

You need a air space at the top of the tank to allow for the expansion when the heat is on. You might want to shut the water down, open the relief valve then the drain valve. bleed off some of the water. Close the relief then drain valve. Put the water back on, open a hot water faucet and bleed off the excess air. You should be go to go. If it still leaks, replace it. I will not repair it self. It will only rust up the inside of the hot water heater and make stains down the side of the RV. Bill

othertonka

Stockton, CA

Senior Member

Joined: 11/15/2003

View Profile


Posted: 06/01/08 06:13pm Link  |  Quote  |  Print  |  Notify Moderator

I have found that there could be a little piece of lime scale under the seat. Caused by hard water. I have flicked the lever a few times letting a little water escape each time to maybe flush the seat clean and then letting the lever "Snap" back closed. It has worked for me. But if it still leaks, a replacement is in order. I have never tried to replace a "Seat" and do not even know if it can be done. A new valve can not be that expensive, but try the "Flicking" first, you might get lucky.


Othertonka
2004 Southwind 32VS
2002 CRV Toad
U. S. Gear Unified brake system
Retired Fire Captain, SFD


wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile

Offline
Posted: 06/01/08 08:42pm Link  |  Quote  |  Print  |  Notify Moderator

You said it was a slow but steady drip and the burner was on.

Let me make a wild stab at a guess here:

You are hooked up to city water and DO NOT use a pressure regulator

Am I right? Yes: Read on.. NO: skip to next reply

City water can often go as high as 100 PSI or more, (NOTE that PEX tubing has no problem with this but the seals on the flush valve for your toilet... NOT SO FORGIVING and a female of the canine flavor to replace)

What has happened is that the city forced too much pressure (80 psi is more common) into your RV's system.. There is, of course, a check valve on the city side.. As the water heats in the hot-tank it expands. since a liquid can not be compressed the only thing left to compress is the air-"head" or cusion on the water heater tank and, of course, the anti-hammer pipes (if any) on the faucets.

The pressure has gone up, since it was too high to start with, it went up BEYOND the relief point on the TPR valve

Soultion.. A Watts or equal whole house pressure regulator set at 45 to 50 PSI on the water inlet of the rig. NOT the more common "Marshall Brass" type, but a Watts whole house type.. Lowes, Home Depot, Selected RV stores including Selected (NOT ALL ) Camping world stores (IT is not a CW catalog item far as I know but some stores have 'em)


Nothin adds excitment like something that is none of your business
John is Near Kenwood TS-2000 housed in a 2005 Damon Intruder 377


smkettner

Southern California

Senior Member

Joined: 03/21/2005

View Profile

Online
Posted: 06/01/08 08:56pm Link  |  Quote  |  Print  |  Notify Moderator

I would replace it and get a small Shurflow expansion tank. Most are rated 150 psi and your plumbing may well be rated 100 psi like mine.


2001 F150 SuperCrew 5.4 Lariat Offroad 4x4 Tow Package 4.10 Truetrac
2006 Keystone Springdale 249FWBHLS
12K SuperGlide, KGE3000Ti 2.3kw rated 2.6kw max
Frank's voltage booster, Prosine 1800 powered by 4 GC2 batteries

VDOCAD

Arcadia, CA

Senior Member

Joined: 04/07/2006

View Profile

Offline
Posted: 06/01/08 08:58pm Link  |  Quote  |  Print  |  Notify Moderator

Mine was also leaking and replacing it with a new one fixed it.

joshjack

Alabama

Senior Member

Joined: 11/01/2007

View Profile

Offline
Posted: 06/03/08 06:57pm Link  |  Quote  |  Print  |  Notify Moderator

Well I was connected to park water without a regulator - guess I should start using that regulator I've got in the toolbox...

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Tech Issues

 > Leaky hot water relief valve
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2008 RV.Net | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS