I just installed SunGuard windshield covers & used the metal snaps, I am plugged in to 50 amp & when I am on an aluminum ladder I get a pretty good shock when I touch one of the snaps.
Anyone ever experience this?
|
JConatser

Smyrna, Tennessee, USA

Senior Member

Joined: 05/04/2004

View Profile

Offline
|
This should not be happening, and the way you describe it, it is potentially life threatening. I would advise you to have someone who knows electricity find out what's going on and fix it. Immediately.
Ameri-Lite 24RB
1997 Chevy 1500 Ext Cab, 5.7L
Equal-i-zer Hitch
|
cmartin7143

ILL

Senior Member

Joined: 01/01/2008

View Profile

Offline
|
Any good with a volt/ohm meter? Are you using an extension cord or adapter? Your coach frame is HOT. Causes are mostly from the above or a improper receptical. it can be as simple as the extension cord is plugged in poorly. plugs and recepticals are polerized. one blade is hot, one is neutral (done by size) the last one is ground. if you stick your meter probe into a known good ground (Ie, wet dirt) and the other to bright metal on the coach you can read the voltage. Make it disapear! the problem is real common in older campgrounds.
good luck.
ops! you have 50amp two hots one ground. same problem.
* This post was
edited 09/13/09 09:11am by cmartin7143 *
|
alfredmay

West Milford, NJ / Donna, TX

Senior Member

Joined: 05/18/2002

View Profile


Good Sam RV Club
Offline
|
I had this happen and it turned out to be an adapter. It was made in China and the wires inside of it must have been reversed at the factory. When I changed the adapter my problem went away.
Alfred May
2005 Excursion V10 4.30 4x4
2002 Cedar Creek 30RBS TT by Forest River
Reese Dual Cam
Tekonsha Prodigy
|
Jamesrpm

Oregon Coast

Senior Member

Joined: 08/30/2003

View Profile

Offline
|
Just one snap in particular ? Or all of them ? Might be a screw into a wire.
___________________________________________
I plan on living forever , so far , so good
|
|
|
pulsar

Lewisville, NC

Moderator

Joined: 12/30/2001

View Profile


Good Sam RV Club
|
Moved from Technology Corner to Tech Issues.
|
wolfe10

Texas

Senior Member

Joined: 10/08/2000

View Profile

Offline
|
Start by testing the CG outlet:
outer straights are hot
middle straight is neutral
middle round is ground
So outer to either middle= 120 VAC
middle to middle= zero
outer to outer= 240 VAC
If that is OK, check out same on RV end of shore power cord.
If that is OK, check at ATS.
Brett Wolfe
1993 Foretravel 36' U-240
Cat 3116, Allison 3060
Caterpillar RV Engine Owner's Club: www.catrvclub.org
|
Wayne Dohnal

Bend, OR.

Senior Member

Joined: 03/09/2003

View Profile

Offline
|
Here's another current thread talking about probably the same thing Electrical issue - 50 Volts to Ground . Unless as one post suggested you might have been unlucky enough to penetrate a wire with the snap's mounting screw or nail.
2009 Fleetwood Icon 24A
LinkPro battery monitor
EU2000i generator
|
T_Bone

Arizona

Senior Member

Joined: 09/20/2001

View Profile

|
cmartin7143 wrote: ... ops! you have 50amp two hots one ground. same problem.
Hi cmartin,
So where does one get a NEC approved 120v circuit from using your above statement?
T_Bone
02 F350, 4x6, CC, DRW, PSD, 6spd, 3:73
32ft Serria 10yr 100% Solar
Please do not trust everything you read on the internet. Use only valid engineering information from well established Companys.
Buy UNION Work UNION
It pays off in the long run !
|
big dave

Soldotna, Alaska, USA

Senior Member

Joined: 12/15/2001

View Profile

Online
|
I would measure the voltage from that snap to a good ground on the frame. As others have said, you probably found a wire with the snap screw.