A question for you experts. When I start the generator the GFI trips. I can reset it and it is fine the rest of the time the generator is running, on shutdown, and when connecting to shore power. Any ideas on what would cause the GFI to trip when starting the generator and work fine the rest so the time?

Thanks

john&bet

North Vernon,in.

Senior Member

Joined: 03/18/2007

View Profile





Offline
Posted: 12/27/11 02:44pm Link  |  Print  |  Notify Moderator

Where is the gfi located and what load/s are on it when generator is started? More info needed.


2004.5 Dodge 2500ctd Quadcab. Lariamie, 3.73, auto. pure stock
2005 Montana 2955 5er


Wayne Dohnal

Bend, OR.

Senior Member

Joined: 03/09/2003

View Profile


Offline
Posted: 12/27/11 11:45pm Link  |  Print  |  Notify Moderator

Do you have an automatic transfer switch? Maybe something is glitching during the shore-to-generator transition.


2009 Fleetwood Icon 24A
Honda Fit dinghy with US Gear brake system
LinkPro battery monitor - EU2000i generator

ELF of WA

Washington

New Member

Joined: 12/07/2010

View Profile





Offline
Posted: 12/28/11 05:38am Link  |  Print  |  Notify Moderator

Wayne Dohnal wrote:

Do you have an automatic transfer switch? Maybe something is glitching during the shore-to-generator transition.


After it was first happening I did replace the GFI but it is still occurring. I am thinking about the transfer switch. I have been disconnecting shore power prior to starting the generator so the transfer switch is not actually transferring. However, I was having a problem with one of the transfer switch relays not picking up. It seemed to be stuck. I fixed that so now both pick up but this GFI issue is still there. I was wondering if the previously sticking relay could have something to do with this GFI issue.

ksg5000

Oregon

Senior Member

Joined: 06/30/2008

View Profile



Posted: 12/27/11 07:37pm Link  |  Print  |  Notify Moderator

My experience is that GFIs get flaky over time - I would install a new one and see if the issue goes away.


Kevin

ELF of WA

Washington

New Member

Joined: 12/07/2010

View Profile





Offline
Posted: 12/27/11 04:27pm Link  |  Print  |  Notify Moderator

john&bet wrote:

Where is the gfi located and what load/s are on it when generator is started? More info needed.


The GFI is in the bathroom, however the circuit covers the bathroom, kitchen, dining and outside outlets. As far as loads, there is no load to speak of. The microwave is plugged in but not running aside from the clock and a night light is on in an outlet in the bathroom.

tempforce

Pacific Wonderland (in the summers)

Senior Member

Joined: 04/26/2002

View Profile


Offline
Posted: 12/28/11 10:46am Link  |  Print  |  Notify Moderator

you may be getting a surge in the gfi, do you have anything turnned on in the circuit when transfering power?


somewhere in the texas 'lost pines'
'08' Dodge mega limo-cab, 409, kelderman rear air ride, max brake controller.
'02' 34' Holiday Rambler TT, the Gypsy Wagon.
'83' Ford Ranger with a 2.2 Diesel, little smoke
'56' F100 project truck


This Topic Is Closed  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Tech Issues

 > GFI trips when genset starts
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2013 RV.Net | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS