Just replaced the analog stat in the 5er.
Dometic AC / Suburban Heater. Heres the situation
Heater works fine cycles on and off at set temp, Checked with seperate Thermometer.
When I tried the AC it calls for AC but unit does not run, no compressor no fan.
Changed back to the analog all is well,
I did have to put the analog stat all the way to lowest setting for ac to come on though. (40 Degrees on stat)
Camper was 65 Degrees inside outside temp 48 degrees.
Hunter stat only goes down to 45 Degrees.
Wired per hunter mods here on the net.
only hooked the blue wire for high fan as I dont have A switch yet for the hi / lo fan
Hunter is wired as follows
Red 12 volts not used
Tan lo fan not used
Blue to hi fan
White to Furnace
Yellow to AC Comp
Green(was ground) to RC
RC RH switched has jumper connected
Any suggestions would be appreciated.
2013 Cedar Creek 38 FL
2003 GMC 3500 DRW 8.1 / Allison, 4:11 4x4
Reese 16K Hitch, Prodigy Brake controller
Carol, Kirk & Nicholas 4YO Grandson we are raising
CAUTION! Behind this Truck is A contagious Disease, NO KNOWN CURE!!!
Its Called Camping!!!!!!
|
enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile


|
What is model of the old thermostat?
What is the model of the new thermostat?
Bud
USAF Retired
Suzuki XL7 pushing Pace Arrow
|
Chris Bryant

DeLand, Florida, USA

Senior Member

Joined: 03/26/2003

View Profile

|
You must hook up both tan and blue for high fan, or just tan for low fan (just blue will not work). and I bet it was too cold to kick the compressor in.
-- Chris Bryant
My RV Service Blog
The RV.net Blog
|
Old-Biscuit

Across the USA

Senior Member

Joined: 06/20/2009

View Profile

|
If rig temp was 65*F then if you set the temp for 63*F you should hear a click then AC should start.........how long did you wait for it to come on? Outside temp wouldn't matter. If I have cycled my A/C I have to wait for minute or longer after I hear 'click' at thermostat before A/C will restart.
Your wiring is correct for the Dometic (Duotherm A/C)/Atwood Furnace.
The other wiring diagram I have seen is for Coleman/Atwood
On Edit: missed tan was NOT connected....
|
ScottG

Bothell Wa.

Senior Member

Joined: 02/25/2005

View Profile

Offline
|
Chris Bryant wrote: You must hook up both tan and blue for high fan, or just tan for low fan (just blue will not work). and I bet it was too cold to kick the compressor in.
This is what I was thinking from my install.
Scott, Grace and Wesly
2003 Dodge 3500 4x4, 6 speed Cummins (lightly bombed),
2004 Forest River 25RKS many, many mods.
H0NDA eu2000i
|
|
|
Old-Biscuit

Across the USA

Senior Member

Joined: 06/20/2009

View Profile

|
Chris Bryant wrote: You must hook up both tan and blue for high fan, or just tan for low fan (just blue will not work). and I bet it was too cold to kick the compressor in.
Outside temp to cold to kick compressor in......is there some sensor other than freeze probe on evap fins???
|
ronfisherman

SE Michigan

Moderator

Joined: 06/05/2006

View Profile


Good Sam RV Club Member
Online
|
The Hunter Thermostat I have has 2 positions for AC. You must push it down to the lowest position to get AC. There is also a 15 minute delay for restart of AC after it has been turned off then back on.
2004 Gulf Stream Endura 6340 D/A
TST tire pressure monitor system
Kodiak Chassis Class C Forum
|
ronfisherman

SE Michigan

Moderator

Joined: 06/05/2006

View Profile


Good Sam RV Club Member
Online
|
Double post.
|
kirk37r

Millville, New Jersey

Senior Member

Joined: 09/23/2007

View Profile


Good Sam RV Club Member
Offline
|
THANKS Chris!!!
Just came back in from Camper, switched the blue to the tan and the AC fan came right on, No compresser like you said. I guess thats ok for the temps right now. As I know the AC works fine.
Thanks Kirk