Posted: 03/27/12 01:24am Link  |  Print  |  Notify Moderator

I have a newer Marshall Brass Extend-A-Flow tee on my coach. It's been perfect for two years, using portable 20-lb bottles to keep me warm. I routinely swap out bottles without trouble.

Lately, I thought I had a bad regulator or clogged supply line, but that seems not to be the problem. It turns out, when I notice the water heater running a flame more like a Bic lighter, or the catalytic heater giving off very little heat, that the "excess flow" protection has triggered. (And, of course, the big furnace won't even light with such low gas pressure.)

Once I shut everything off and allow it to reset, we're back to normal. At least for a while. So my question is: in the absence of any "excessive flow," why is the excess flow protection protecting me? Is this a known failure mode? Is this the beginning of the end for my Extend-A-Flow?

I don't have a leak, I don't have excessive flow, and I'm not doing anything different. Is a new tee in my immediate future?

I THINK the excess flow protection is contained in the POL at the regulator side of the tee -- I guess I could just replace that? The benefit of your experience will be appreciated.


Wayne
Fulltimers
1999 Damon Intruder 341

eHoefler

ozark mountains

Senior Member

Joined: 10/22/2011

View Profile


Offline
Posted: 03/27/12 05:38am Link  |  Print  |  Notify Moderator

Actually it is in the valve on the bottle. If you open it too quickly, you can activate it. If your demand is too great, it can trip it. The water heater and the furnace are the greatest demands on you propane. If it is close to the valve rating, anything else on may trip it while the furnace and water heater are running.


2010 Ram 3500, Crew Cab, Long bed, 4 x 4,Dually, Lights & Siren!

2006 40' Landmark Mt. Rushmore

shooted

Vancouver

Full Member

Joined: 06/17/2011

View Profile



Posted: 03/27/12 09:01am Link  |  Print  |  Notify Moderator

I had the same problem a couple of years ago. Replacement of the hose between the automatic change over and the tank fixed the problem. I believe the excess flow valve would be designed to fail in a safe mode.

red31

Bryan

Senior Member

Joined: 08/04/2008

View Profile


Offline
Posted: 03/27/12 06:22pm Link  |  Print  |  Notify Moderator

What kind of junk can cause the excess flow to clog or malfunction?

Ain't that little ball the excess flow device and the white thermal bushing melts at high temp allowing the valve to close?


Ex-Tech

West

Senior Member

Joined: 08/27/2011

View Profile



Posted: 03/27/12 05:25pm Link  |  Print  |  Notify Moderator

eHoefler wrote:

Actually it is in the valve on the bottle. If you open it too quickly, you can activate it. If your demand is too great, it can trip it. The water heater and the furnace are the greatest demands on you propane. If it is close to the valve rating, anything else on may trip it while the furnace and water heater are running.


Actually, it is not in the valve at all. The Overflow Protection Device is contained within the POL/Acme fitting on the end of the rubber propane hose that screws into the valve.
The only safety devices contained in a portable tank valve is the Overfill Protection Device float valve and the high-pressure safety release valve.
(This is why the poster above (shooter) fixed his problem by replacing the propane hose).

This also why, when a tech needs to empty a propane tank, he can screw a blank POL fitting into the tank to activate the check-valve and then open the valve and purge the tank releasing full, non-regulated pressure. Done this a few times myself.

BTW, the POL/Acme fitting and hose assembly also usually contains a temperature activated device that shuts down flow in the event of a fire.

* This post was edited 03/27/12 05:36pm by Ex-Tech *

This Topic Is Closed  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Tech Issues

 > Extend-A-Stay Excess Flow Works Too Well
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2013 RV.Net | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS