View Profile

Offline
|
The tstat still seems sense the temperature because the burner fires only when it cools down, however as soon as i turn on the furnace the fan runs until i shut off the furnace by switching the switch from auto to off.
I'd rather be in a boat with a drink on the rocks, then in the drink with a boat on the rocks!
|
Earl E

Green Valley, AZ

Senior Member

Joined: 04/16/2007

View Profile


Good Sam RV Club Member
Offline
|
Every rig I have had has two switches. One is "Heat/Off/AC". The other is Auto/On. You want Heat and Auto, then it should cycle. Heat/On will run the ac fan continuously. That may be what you are hearing. Just make sure the one switch is on Heat, the other on Auto.
2007 Northwoods Arctic Fox 32 5S Fifth Wheel-for sale now that we are not full-timing
2011 Keystone 23rks Hideout to poke around the smaller parks in the great Southwest
2007 Chevy Silverado 2500 HD Diesel
Prodigy brake control
|
bartlettj

Forest Grove, OR

Senior Member

Joined: 04/24/2012

View Profile


Good Sam RV Club Member
Online
|
The system I have (Dometic) has a digital thermostat with fan, cool, and heat modes. If you set the fan mode to anything other than auto, it runs all the time.
|
dan-nickie

Grand Prairie, TX

Senior Member

Joined: 02/11/2011

View Profile


Good Sam RV Club Member
Offline
|
I beleive on most systems, the fan runs 'a while' after the burners go out to cool down the ducts, etc. Same on my home system.
How patient have you been to see if the fans will turn off by themselves?
I believe, in a way, it does monitor the duct temperature when the burner is off to keep the system from overheating internally. Either that or it has a timed delay.
Dan and Nickie, Four Winds 31p, Retired Jan/2011
|
jetenbu

Southeast Texas

Senior Member

Joined: 08/03/2006

View Profile


Good Sam RV Club Member
Offline
|
I believe the key is to make sure you have the fan on Auto so that it can cycle on/off properly. This is the way mine works on both heat and a/c.
Jim
RV: 2012 Montana 3625RE Quad Slide SKP#108921
TV: 2004.5 Dodge Dually 3500 HD
Favorite Quote: ''Life's tough, pilgrim, and it's even tougher if you're stupid.''-- John Wayne
Warning: THIS RIG PROTECTED BY SMITH AND WESSON!
U.S. Navy Vietnam Vet 1967-1968
|
|
|
JJBIRISH

Butler, PA, USA

Senior Member

Joined: 10/06/2002

View Profile


Good Sam RV Club Member
|
It sounds like there might be a air flow problem for the furnace…
The duct system is not broadcasting the heat into the room fast enough causing the heated air in the distribution box to get hot enough for the limit switch to shut the gas down before the t-stat is satisfied (short cycling)… when the air in the distribution box cools the limit switch allows the burner to relight…
I believe you will find the auto switch on the t-stat operates the ac fan…
Love my mass produced, entry level, built by Lazy American Workers, Hornet
|
INDIAN CREEKER

Full Timers, We're always home!

Senior Member

Joined: 05/12/2006

View Profile


|
tzclark wrote: The tstat still seems sense the temperature because the burner fires only when it cools down, however as soon as i turn on the furnace the fan runs until i shut off the furnace by switching the switch from auto to off.
I had the same type of problem on a Dometic thermostat. I had to switch to fan mode. Then make sure that in fan mode the fan was set to auto rather than high or low. No more trouble. Hope this helps.
Dave
Dave and Linda
2012 Salem Park Trailer
Navy VietNam Vet, Dong Ha Ramp 68-69
|
JoyceandSteve

Houston, Texas

Senior Member

Joined: 05/24/2011

View Profile


Good Sam RV Club Member
Offline
|
bartlettj wrote: The system I have (Dometic) has a digital thermostat with fan, cool, and heat modes. If you set the fan mode to anything other than auto, it runs all the time.
I could be toatally off base, but I beleive thats what it is suppose to do??? OP poster may have a t-stat problem or is it wired correctly?
Steve & Joyce
2011 Chevrolet 2500 Z71 4X4
2013 Montana High Country 343 RL
1996 Celebrity 200 Boat
2000 Yamaha 1200 LTD Waverunner
2012 Ford Mustang GT (Mama's ride)
Vítejte na víkend doma a Steve Joyce
|
JJBIRISH

Butler, PA, USA

Senior Member

Joined: 10/06/2002

View Profile


Good Sam RV Club Member
|
I have never had one that worked that way…
The FAN switch is wired as AUTO/ high cool/ low cool, or ON high cool/ low cool… and controls the AC fan, I have never had one that controls the furnace fan… the furnace fan is a single speed fan that operates the sail switch and circulates a predetermined volume of air…
I sounds like his furnace is short cycling and the time delay switch keeps the fan running between short cycles…
That to me would indicate a air circulation restriction either at the intake or in the hot air distribution…
|
tzclark

Chilliwack

New Member

Joined: 08/06/2011

View Profile

Offline
|
Ok, so I tested it today again. I am not sure if the stat is actually sensing temp, however I can hear the high limit snapping. The fan and the ducts seem good, lots of air through them. I am going to replace the stat and the high limit and see if that solves the problem. By the way it's a duotherm stat and suburban furnace if that helps anyone.
|
|
|