I'm eventually going to upgrade to one. I just happen to have a 12V one. I'm going to use a 12V power supply on the shore side to facilitate the switching.
Verify if your inverter has a neutral-ground bond. If so, your schematic should work. To verify: with the inverter disconnected from the battery, use a multimeter set to measure resistance at it's lowest setting (or if it has continuity test setting use that). Check between the neutral and the ground connections. Should read zero or pretty close to zero. If it doesn't read anything, then you don't have a N-G bond and will need to provide it on the inverter side of the switch. If you don't have the N-G bond, you will have an open ground situation which is a safety issue. Do not bond the neutral to the ground anywhere else except at the inverter.
2004 Toyota Tundra SR5 (V8, 4WD, TP, TRD)
2005 Fleetwod Allegance with axle flip
Honeywell 2000i Generator
Me, DW, DS, DD, Dog & Camping Kitty
Thanks James. I have one more question: If I were to use a SPDT relay instead, could I tie the neutral from shore mains to neutral on the inverter? I come from the 12VDC world thinking this would be like tying ground common. Of course only if the ground and neutral don't connect on the inverter.
I if build a new rig from the ground up, that's the system I will be using. I'm just trying to get functionality with the hardware I have without spending more than I have.