RV.Net Open Roads Forum: Tech Issues: Adding a Second 50A Transfer Switch

RV Blog

  |  

RV Sales

  |  

Campgrounds

  |  

RV Parks

  |  

RV Club

  |  

RV Buyers Guide

  |  

Roadside Assistance

  |  

Extended Service Plan

  |  

RV Travel Assistance

  |  

RV Credit Card

  |  

RV Loans

Open Roads Forum Already a member? Login here.   If not, Register Today!  |  Help

Newest  |  Active  |  Popular  |  RVing FAQ Forum Rules  |  Forum Help and Support  |  Contact

Search:   Advanced Search

Search only in Tech Issues

Open Roads Forum  >  Tech Issues

 > Adding a Second 50A Transfer Switch

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 4  
Next
Sponsored By:
mena661

Southern California

Senior Member

Joined: 03/21/2009

View Profile


Offline
Posted: 07/13/12 01:02pm Link  |  Quote  |  Print  |  Notify Moderator

My "new" MH has a 50A transfer switch (generator and shore power). I want to add in my inverter (whole house) and install a second ATS but I'm not exactly sure where I should install it. My thinking is the best/easiest would be to install on the shore power side of the OEM ATS. What do you guys think? BTW, I won't be able to inspect the unit itself till tomorrow at the earliest.


2009 Newmar Canyon Star 3205, Ford F53 V10
Trojan L16 6V's 740 Amp-hours


dougrainer

Carrolton, Texas

Senior Member

Joined: 06/11/2007

View Profile


Online
Posted: 07/13/12 01:31pm Link  |  Quote  |  Print  |  Notify Moderator

The Inverter is NOT a 50 amp Inverter. They usually ONLY transfer 30 amp service and that is the PASS thru rating. The Inverter should have its OWN 30 amp transfer switch. You do realize that a 50 amp RV and 50 amp transfer switch actually transfers 100 amps total? You NEVER install an Inverter and run the complete RV shore or APU power thru it. The Inverter is NOT rated to do that. Doug

wolfe10

Texas

Senior Member

Joined: 10/08/2000

View Profile


Online
Posted: 07/13/12 01:33pm Link  |  Quote  |  Print  |  Notify Moderator

What is inverter output. Depending on its output and what you want to run from those inverter-supplied circuits, a 30 amp (single HOT) is what you need.

Give us more details on your system and what you want to do and we may be able to help.


Brett Wolfe
1997 Safari Sahara 3540
EX: 1993 Foretravel 36' U-240


FMCA Forum: www.community.fmca.com/index

Diesel RV Club:http://www.dieselrvclub.org/

smkettner

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 07/13/12 01:34pm Link  |  Quote  |  Print  |  Notify Moderator

What is the priority order?

1 Generator
2 Shore
3 Inverter

Or something else?


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675 watts solar
Send a PM if I missed something

mena661

Southern California

Senior Member

Joined: 03/21/2009

View Profile


Offline
Posted: 07/13/12 01:59pm Link  |  Quote  |  Print  |  Notify Moderator

300W inverter currently that will be upgraded to a 2000W. Want to run whole house, no sub panels. Don't have a problem with remembering to switch stuff off or just plain not use it as that's what we do now (besides where we camp, accidentally running the A/C on a 300W inverter won't happen). I prefer the simplicity and cheaper cost of wiring whole house. 2000W inverter would run MW and maybe the convection oven too (it only has a convection oven) plus all receptacles. The coach has tube fluorescent lighting that I'm not sure if it's 120V or 12V. If it's 120V then I'll be running that from the inverter too.

smk,
Hmmmm. Probably...
1. Inverter
2. Generator
3. Shore

But would it make more sense to make sure the inverter is on the normally closed side of the both ATS's?

smkettner

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 07/13/12 02:14pm Link  |  Quote  |  Print  |  Notify Moderator

If you put the inverter on the normally closed side, the TS will switch power to the other source when present. This will not give inverter #1 priority.

I would think if you were on inverter and started the generator you would want generator power for example. Yes you can turn off the inverter but still it is not really first priority.

Although there might be other reasons to stay on inverter while the generator charges the battery. Could reset some electronics when the TS switches.

Just stuff to think about.

* This post was edited 07/13/12 02:26pm by smkettner *

MrWizard

Traveling

Moderator

Joined: 06/27/2004

View Profile



Posted: 07/13/12 02:31pm Link  |  Quote  |  Print  |  Notify Moderator

better look at your ATS before you decide what to do

my 50 amps ATS has (2) relays, one for shore, one for generator
each one operated by power from that input line, and there is a mechanical interlock between them, that is operated by whichever side is energized to prevent the other side from pulling in

do you really want the constant drain of an ATS relay powered by the inverter
too avoid this i think you will need a manual switch 4 pole switch rated for 50amps placed between the shore side of the OEM ATS and the new inverter

output side of the switch to the house, the two inputs one from the inverter, and one from the existing output of the shore side of the ATS


Options, always have options, and the journey goes much smoother
....

Connected thru Verizon with HotSopt WiFi using a Samsung Galaxy Nexus
Member of the Verizon Wireless Customer Council
I BOUGHTthis phone


2oldman

Winchester WA

Senior Member

Joined: 04/15/2001

View Profile


Offline
Posted: 07/13/12 02:38pm Link  |  Quote  |  Print  |  Notify Moderator

mena661 wrote:

best/easiest would be to install on the shore power side of the OEM ATS.
I'm not by any means an expert on 50a. I picture this installation as being 'just another 30a ac source' like when you only have a 30a socket at the CG. How does that work? I would find which wires that service utilizes, and stick the inverter there.

I'm also not too familiar with OEM ATSs.. my vision is an inverter with its own ATS.

DryCamper11

Hartford

Senior Member

Joined: 05/08/2012

View Profile


Offline
Posted: 07/13/12 02:39pm Link  |  Quote  |  Print  |  Notify Moderator

On mine, I bought two 30A contactors and a 6 second delay relay from Grainger's to make two Transfer Switches - TS#1 and TS#2 - in a single box. The generator and shore power were connected to TS#1 and it switches before the AC panel to power the entire RV. If the generator runs, it drives the delay relay and 6 seconds after it sees good steady AC power, the delay relay fires the contactor for TS#1 and the whole RV switches to gen power.

TS #2 is after the panel on the single circuit that runs all the 120V plug-in sockets (except AC, refrigerator and converter). When I installed it, the AC was already on a separate circuit and I added two other separate circuit breakers for the converter and refrigerator. The refrigerator required running another AC line. That was the hardest part. The converter was integrated into the bottom half of the AC circuit breaker panel and I just needed to add two more breakers and move one wire.

When I turn on the inverter, TS #2 fires immediately and all the 120VAC sockets are on the inverter. It's worked great for the last 20 years.


In the Boonies!

DryCamper11

Hartford

Senior Member

Joined: 05/08/2012

View Profile


Offline
Posted: 07/13/12 02:57pm Link  |  Quote  |  Print  |  Notify Moderator

MrWizard wrote:

my 50 amps ATS has (2) relays, one for shore, one for generator each one operated by power from that input line, and there is a mechanical interlock between them, that is operated by whichever side is energized to prevent the other side from pulling in

That seems like an odd design. There's no default position. It seems that if both were off - no shore and no inverter, nothing would be connected.

Are you sure it works that way - one relay for gen and one for shore?

It would work with that design, but I think it would be more costly. You'd need to switch both phases with each relay, although you could use single throw relays. If I saw two relays in a 50A ATS I'd suspect one was being used for each 120VAC side of the 50A/240V power source. That would only need to switch one phase for each relay, but you'd use double throw relays.

The default position would be both relays off - sending shore power on both sides. If the generator came on, I'd expect both to pull in, switching both phases, with a common interlock to make sure they both pull in or drop out together.

I've never seen a 50A ATS, which is why I ask.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 4  
Next

Open Roads Forum  >  Tech Issues

 > Adding a Second 50A Transfer Switch
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2013 RV.Net | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS