Posted: 04/19/08 09:56pm Link  |  Print  |  Notify Moderator

I am installing a new 50A service for the MH and am looking for electrician advice on sizing the neutral. The distance between my house main panel and the new 50A receptacle will be 143'. Calculating voltage drop assuming a full 50A load I have determined I need to use #2 wire for the two 120V hot wires (this results in a voltage drop of 2.87%).

Question is this, since my MH is utilizing two independent 120V services and there are no 240V loads, how do I size the neutral wire to accommodate unbalanced loads? Can I use #2 wire for the neutral or do I need something larger?


2007 National Seabreeze 1321
Ford F53, 6.8L V10


WayneZat

Tucson, AZ

Senior Member

Joined: 04/17/2004

View Profile


Posted: 04/19/08 10:06pm Link  |  Print  |  Notify Moderator

I haven't looked but I would say no, it #2 carries the load, you can only pull 50 amps then your breaker trips. Your breaker will trip at 50 amps not 100, and I don't see where you will ever pull the full 50 amps.

smkettner

Southern California

Senior Member

Joined: 03/21/2005

View Profile

Offline
Posted: 04/19/08 10:09pm Link  |  Print  |  Notify Moderator

Neutral should be the same size as the hot connections.
http://www.myrv.us/electric/

Hurricaner

Hurricane Utah

Senior Member

Joined: 02/17/2007

View Profile


Posted: 04/19/08 10:14pm Link  |  Print  |  Notify Moderator

The neutral can be sized the same as the hots as it is impossible for it to carry more current under normal operating conditions. I would also use 240 volts for your calculations. Although it is possible for a 50 amp service to use 120 volts exclusively, it is highly unlikely especially at anything over 30 amps. I would use #4 for that distance, #2 is overkill.

Sam


Sam & Kari
Hurricane, Utah


2004 34' Damon Challenger 315

Chris Bryant

DeLand, Florida, USA

Senior Member

Joined: 03/26/2003

View Profile


Posted: 04/20/08 06:59am Link  |  Print  |  Notify Moderator

Nope- the most the neutral will every carry is 50 amps, and that is unlikely, though possible.


-- Chris Bryant
My RV Service Blog
The RV.net Blog

Roadpilot

Lakes Region of New Hampshire

Senior Member

Joined: 09/16/2006

View Profile

Offline
Posted: 04/20/08 07:00am Link  |  Print  |  Notify Moderator

The two hot wires on 50 amp service are out of phase, i.e. 180 degrees out of phase. Therefor the two neutral currents are subtracted. If the loads on each phase were perfectly balanced, the neutral current would be zero.

As an example, say you have to matched AC units, one on each phase, each drawing 12 amps. Each hot would measure 12 amps, but the neutral would measure zero amps.

If the campground were wired incorrectly or possibly a long time ago, the two hot wires may not be out of phase. If this were the case, the neutral currents would add. In the example above, each hot would measure 12 amps and the neutral would measure 24 amps. The breaker is in the hot lead, not the neutral, so it wouldn't be able to protect against this problem.

They sell inexpensive checkers that will tell you if the 50 amp service is wired correctly.

Bottom line is use the same size wire for the neutral as the hot wire, because you could have a load on only one phase so the neutrals wouldn't cancel. Then just in case, buy a checker.


2007 Newmar Essex 45'
2006 Honda CR-V and 2005 Chevy Silverado 1500
2004 HD Electra Glide Ultra Classic
2006 HD Heritage Softail Classic
Overbilt Lift

enblethen

Moses Lake, WA USA

Senior Member

Joined: 01/05/2005

View Profile


Posted: 04/20/08 07:30am Link  |  Print  |  Notify Moderator

The grounded conductor (neutral carries only the unbalanced loads.
Sizing should be calculated same as the feeder circuit. Yes, you could downsize by calculating this number.
"Exception: For 3-wire, 2-phase or 5 wire, 2 phase system, the maximum unbalanced load shall be the maximum net calculated load between the neutral and any one ungrounded conductor multiplied by 140 per cent" NEC article 220.61
I would not recommended downsizing in an RV application to start with. Newer products using heavy non-linear loads such as converters, inverters, and fluorescent fixtures throws out a bunch of harmonics.
I would suggest you add an additional receptacle, a 15 or 20 ampere GFCI at the RV end. It comes i handy for work lights, drills or such.


Bud
Suzuki XL7 pushing Pace Arrow



dontay

Mims, Florida

Senior Member

Joined: 03/22/2003

View Profile

Offline
Posted: 04/20/08 07:32am Link  |  Print  |  Notify Moderator

I agree that the #2 wire is way overkill and over-expensive. I used #4 from the house 220' to the workshop for 60 amp 240 V service. From the workshop to the RV garage I used 110' of #6 for the 50 amp service.
We are living in the MH while building a new house so we are at the end of a 65' 30 amp extention cord since we don't want to be in the garage except during storms. (Waiting delivery of a 50 amp extention cord.) But even with all that length the AC Volt meters I installed in the MH (see pictures on webshots) never drop below 110 Volts with one a/c running. One time it droped down to 100 V when I turned on the a/c but switching the water heater from 110 V to gas made the voltage rise back to 110 V.

50 amp service is really two 50 amp lines wired to 240 V. I do not know if any MH's have 240 V appliances. Ours does not. In fact, the generator puts out 120 V on each leg that in in phase with the other. That is if you measure across the legs with a meter you get 0 V. But each is 120 V to neutral.

* This post was edited 04/21/08 12:24am by an administrator/moderator *


ISO9000 Certified Retiree
Mission Statement: ZZZzzzzzzzzz....

2006 Allegro Bay 34XB with Freightliner FRED chassis, 2000 Jeep Cherokee 4x4

http://community.webshots.com/user/longf450

LarryJM

NoVa

Senior Member

Joined: 11/09/2007

View Profile


Posted: 04/20/08 07:58am Link  |  Print  |  Notify Moderator

While it was only 6' CLICKY the 50A range cord that is used for my dual 30A dogbone has two 6Ga (black and red hot sides) and 8ga for the white common and green ground.

Larry


2001 standard box 7.3L E-350 PSD Van with 4.10 rear and 2007 Holiday Rambler Aluma-Lite 8306S Been RV'ing since 1974. TRAILER MODS



Buffalobilly

Holiday Island, AR

Senior Member

Joined: 07/15/2001

View Profile

Offline
Posted: 04/20/08 08:50am Link  |  Print  |  Notify Moderator

I agree that the neutral should be the same size as the legs.
Now there is a know problem with the neutral in most RV boxes. Look at this RV electric. Be sure to read the open neutral section.
Bill


Buffalobilly
95 Safari Sahara
230 B Cummins
pulling a 96 Grand Cherokee


This Topic Is Closed  |  Print Topic  |  Post New Topic  | 
Page of 4  
Next

Open Roads Forum  >  Tech Issues

 > Sizing the neutral for 50A service
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2008 RV.Net | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS