Either THWN individual wires in conduit or Romex UF cable (conduit optional, recommended if rocky), #6 gauge, 3-wire plus ground.
The receptacle you need is the NEMA 14-50R.
I'm free of prostate cancer for 5 years now.
All men over age 50 should get an annual PSA blood test. Mine had a low reading, but the yearly jump was significant. The biopsy showed cancer just entering the aggressive stage. Dr. Hackenslash removed it.
Kenneth wrote: Either THWN individual wires in conduit or Romex UF cable (conduit optional, recommended if rocky), #6 gauge, 3-wire plus ground.
The receptacle you need is the NEMA 14-50R.
I think Kenneth is right on, would just add to use #6 copper, not sure aluminum has enough ampacity, sorry my books are at work.