Posted: 07/29/19 02:48pm Link  |  Quote  |  Print  |  Notify Moderator

Hello,
When I plug my electric cooktop into the outdoor GFCI outlet, the GFCI trips. The cooktop is rated at 1000w according to the label. Do those GFCI outlets have a lower amperage rating than normal?

Thanks,
Ray


2016 Avenger 32BIT

Revolver

Winnipeg

New Member

Joined: 08/12/2009

View Profile


Offline
Posted: 07/29/19 02:57pm Link  |  Quote  |  Print  |  Notify Moderator

Revolver wrote:

Hello,
When I plug my electric cooktop into the outdoor GFCI outlet, the GFCI trips. The cooktop is rated at 1000w according to the label. Do those GFCI outlets have a lower amperage rating than normal?

Thanks,
Ray


I should clarify, it doesn't trip immediately when I plug it in. In fact, when I turn the cooktop on it begins to heat but not very much. Then the GFCI trips.

3 tons

CA.

Senior Member

Joined: 03/13/2009

View Profile


Offline
Posted: 07/29/19 03:13pm Link  |  Quote  |  Print  |  Notify Moderator

Revolver wrote:

Hello,
When I plug my electric cooktop into the outdoor GFCI outlet, the GFCI trips. The cooktop is rated at 1000w according to the label. Do those GFCI outlets have a lower amperage rating than normal?

Thanks,
Ray


No, it sounds more like a small amount of internal leakage inside the cooktop, possibly from a cracked element insulator - the GFI is likely reacting to this worn condition..

the bear II

Torrance CA.

Senior Member

Joined: 02/14/2008

View Profile


Offline
Posted: 07/29/19 03:14pm Link  |  Quote  |  Print  |  Notify Moderator

GFCI outlets do go bad often or something in the cooktop once it heats up is causing the GFCI to trip. If you have another GFCI outlet inside the RV try the cooktop in it as a test to see if it trips.

CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile


Offline
Posted: 07/29/19 03:18pm Link  |  Quote  |  Print  |  Notify Moderator

Revolver wrote:

Hello,
When I plug my electric cooktop into the outdoor GFCI outlet, the GFCI trips. The cooktop is rated at 1000w according to the label. Do those GFCI outlets have a lower amperage rating than normal?

Thanks,
Ray
GFCIs are NOT CBs and don't detect over current, but rather an imbalance of amps between the hot and neutral. Try the cooktop on another GFCI and if it doesn't trips - well you know. Otherwise it's the cooktop.


2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob


wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 07/29/19 03:21pm Link  |  Quote  |  Print  |  Notify Moderator

The GFCI OUTLET itself is not current sensitive as far as "Total Anps" is concerned

IT IS. however very sensitive as to amps in v/s amps out. Even a couple mA (1/1000th) of an amp) will trip it if there is any imbalance in the hot and neutral currents.

IN short. your cooktop is the problem. Likely a very tiny hot to case short.

Now a GFCI Circuit breaker (Combination curcuit breaker and GFCI. will trip on overload as well as imbalance.


Home is where I park it.
Kenwood TS-2000 housed in a 2005 Damon Intruder 377


hawkeye-08

Northwest

Senior Member

Joined: 01/25/2008

View Profile


Offline
Posted: 07/29/19 04:53pm Link  |  Quote  |  Print  |  Notify Moderator

My wife's brother and family got rid of the propane outdoor appliances and went to all electric, they set up a table next the trailer and cook away, until a few years ago when it kept tripping the GFCI (it was on bathroom circuit, took them awhile to find it the first time).. they asked me how to figure out what is happening, I said to just run extension cord from power post to cook table.. most power posts have a 20amp outlet next the 30/50 so use it. No more problems..

wopachop

lb

Senior Member

Joined: 11/17/2006

View Profile


Offline
Posted: 07/29/19 05:02pm Link  |  Quote  |  Print  |  Notify Moderator

3 tons wrote:

Revolver wrote:

Hello,
When I plug my electric cooktop into the outdoor GFCI outlet, the GFCI trips. The cooktop is rated at 1000w according to the label. Do those GFCI outlets have a lower amperage rating than normal?

Thanks,
Ray


No, it sounds more like a small amount of internal leakage inside the cooktop, possibly from a cracked element insulator - the GFI is likely reacting to this worn condition..
Can you explain more por favor? Does the crack itself fill with a somewhat conductive liquid causing the hot and ground to tickle each other?

3 tons

CA.

Senior Member

Joined: 03/13/2009

View Profile


Offline
Posted: 07/29/19 05:49pm Link  |  Quote  |  Print  |  Notify Moderator

“Can you explain more por favor? Does the crack itself fill with a somewhat conductive liquid causing the hot and ground to tickle each other?“

wa8yxm has provided a great summary...

Groover

Pulaski, TN

Senior Member

Joined: 10/17/2007

View Profile


Offline
Posted: 07/29/19 08:15pm Link  |  Quote  |  Print  |  Notify Moderator

wopachop wrote:

3 tons wrote:

Revolver wrote:

Hello,
When I plug my electric cooktop into the outdoor GFCI outlet, the GFCI trips. The cooktop is rated at 1000w according to the label. Do those GFCI outlets have a lower amperage rating than normal?

Thanks,
Ray


No, it sounds more like a small amount of internal leakage inside the cooktop, possibly from a cracked element insulator - the GFI is likely reacting to this worn condition..
Can you explain more por favor? Does the crack itself fill with a somewhat conductive liquid causing the hot and ground to tickle each other?


Basically your plug has 3 pins. The power comes in through one blade and is supposed to leave through the other. These are sometimes referred to as the hot and the neutral. For safety in case something breaks and the hot wire touches the same parts that you do (the case) the round pin connects the case to ground so that the electricity doesn't try to go through you to get to ground. The GFI circuit essentially counts the electrons going out through the hot blade connector and compares it with the number coming back through the neutral. If there is a difference it concludes that there is a possibility that the case is charged with electricity and you could be injured so it shuts off the flow of electricity. Many times the device would still work and the leak from hot to the case is taken care of by the ground but just in case you have a ground problem the GFI kills the circuit. There may or may not be "conductive liquid" (water) present but somehow the electricity is finding its way to the case. The best solution is to check the cooktop by trying it on another GFI outlet and replacing it if that GFI trips as well.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 3  
Next

Open Roads Forum  >  Tech Issues

 > Outdoor GFCI outlet trips when using electric cooktop
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2019 CWI, Inc. © 2019 Good Sam Enterprises, LLC. All Rights Reserved. | Terms of Use | PRIVACY POLICY | YOUR PRIVACY RIGHTS