I know it's probably a dumb question but my wife's hair dryer is old and has no equipment ground. Wanted to be sure she is still protected if it should be dropped into water or otherwise shorted.
3 tons
NV.
Posted: 08/20/19 01:54pm Link  |  Quote  |  Print  |  Notify Moderator
The GFI doesn’t rely on a ground, instead it will interrupt power where only a small potential exist between the hot and neutral sides of the receptacle...This is why they are sometimes so dang fussy...
Sam Spade
North Central Florida
Posted: 08/20/19 02:36pm Link  |  Quote  |  Print  |  Notify Moderator
What exactly does that mean ?
A GFCI detects a DIFFERENCE in current flow between the hot and neutral wires. That is, all the current going IN is not coming back OUT on the neutral like it should.....but presumably is finding it's own ground elsewhere.
So....operation with a 2 wire device is a bit iffy.
If the bowl of water it was dropped into is not grounded, then the detector likely wouldn't trip until a persons hand supplied a foreign ground....and maybe not then.
'07 Damon Outlaw 3611
CanAm Spyder in the "trunk"
DFord
Near St Louis, MO
Posted: 08/20/19 02:49pm Link  |  Quote  |  Print  |  Notify Moderator
GFCI outlets measure the power being used on the "hot" power lead and ensure the same amount of power it flowing in the neutral. If a tiny amount of imbalance occurs, it's meant to interrupt the flow of power and keep you safe. If there's no ground wire and you complete a circuit to something that is grounded, it will interrupt just as quickly as if there was one. Some devices don't have a ground wire because they're "double insulated" and you're not supposed to be able to touch a "hot" metal piece on them.
Don Ford
'09 HHR 2LT or '97 Aerostar MiniVan (Remco driveshaft disconnect) for Towed vehicles
Harvard
51.6N 114.7W
Posted: 08/20/19 03:02pm Link  |  Quote  |  Print  |  Notify Moderator
The GFCI would trip the circuit IF the water has at least a capacitive path, if not a conductive path, that would conduct at least 5 mA to Ground. IMO.
time2roll
Posted: 08/20/19 03:10pm Link  |  Quote  |  Print  |  Notify Moderator
Yes an imbalance of 5ma between hot and neutral will trip the GFCI.
Does not matter where the power goes... the imbalance cuts power.
Ground pin is not required for GFCI to trip.
675w Solar pictures back up
Terryallan
Foothills NC
Posted: 08/20/19 03:22pm Link  |  Quote  |  Print  |  Notify Moderator
In truth. The GFCI is NOT there to protect YOU. It is there to protect the circuits. That by doing it's job, it also protects you, is just a bonus
Terry & Shay
Coachman Apex 288BH.
2013 F150 XLT Off Road
5.0, 3.73
Lazy Campers
Chris Bryant
Arden, North Carolina
Posted: 08/20/19 03:43pm Link  |  Quote  |  Print  |  Notify Moderator
Not sure if it still is, but adding a gfci outlet to a two wire system was a code approved way to add an outlet with a ground pin, even though it was not grounded.
-- Chris Bryant
Hurricaner
Hurricane Utah
Posted: 08/20/19 03:58pm Link  |  Quote  |  Print  |  Notify Moderator
yep, still permitted just need to add "no equipment ground" label to outlet.
Sam
Thanks to NECreader who commented on 2016/06/13:
This article should state that NEC 406.3 permits GFCI receptacles to replace two prong ungrounded outlets:
(3) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).
(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter type of receptacle(s).
These receptacles shall be marked "No Equipment Ground." An equipment grounding conductor shall not be
connected from the ground-fault circuit interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the ground fault circuit interrupter shall be marked "GFCI Protected" and "No Equipment Ground." An equipment grounding conductor shall not be connected between the grounding type receptacles.