joe6789

TX

New Member

Joined: 10/10/2019

View Profile


Offline
Posted: 10/10/19 12:17am Link  |  Quote  |  Print  |  Notify Moderator

Trying to install a Multi Plus Compact 2000w inverter/charger in my RV. The shore power connection has four wires: two 50A hot legs (red and black), neutral, and ground. Since the Multi Plus inverter will only power one hot leg, my plan is to "split" my existing breaker panel so that one leg (about half the panel) is powered direct from shore power and the other leg runs through the Multi Plus.

Let's say I leave AC line 1 as the non-inverter side, going straight from shore power into the breaker panel. Then AC line 2 would go from shore power, to the Multi Plus AC-in, then from the Multi Plus AC-out to the second leg of the breaker panel.

But how do I wire the neutral and ground?

Normally AC line 1 and 2 share a neutral and ground (since 1 and 2 are out of phase, their currents cancel each other out on the neutral). But now line 2 gets sent to the Multi Plus while line 1 goes straight to the breaker panel. Is it fine for the neutral and ground wires to simply follow line 2 through the Multi Plus before arriving at the breaker panel? Or does line 1 now need its own neutral/ground? Do I need to split the neutral so that one neutral wire follows AC line 1 into the breaker panel and another neutral wire follows AC line 2 through the Multi Plus? If so, do I need to isolate the two neutrals by cutting the existing neutral bar in the breaker box?

I've read that a better solution is installing a sub-panel, but I'm trying to go for the simplest solution, which I believe would be keeping everything in the existing breaker panel.

Advice would be much appreciated.

larry cad

ohio

Senior Member

Joined: 05/23/2004

View Profile





Offline
Posted: 10/10/19 05:41am Link  |  Quote  |  Print  |  Notify Moderator

All the grounds tie together. Keep in mind that a 2000 watt inverter can only supply about 15-16 amps. A #14 wire can carry that much so your concerns about overloading a neutral are unfounded. However, feeding half of your breaker panel is not necessarily wise. That is why most times the inverter has a separate feed from a 20 amp breaker in the panel, and the output from the inverter is fed to a "sub" panel. Keep in mind that your original panel is also a "sub" panel, meaning the ground and neutral are NOT bonded together in your panel because the ONLY permitted bond occurs at the campground service panel. Hope this helps.


Today is my personal best for most consecutive days alive.

Our Travel Blog

wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 10/10/19 06:54am Link  |  Quote  |  Print  |  Notify Moderator

Proper inverter install

Main panel 30 amp branch----inverter---Sub panel--Inverter powered loads

And that is how it's done on my RV... the sub panel powers the entainerment circuit (includes this computer) GFCI chain (Kitchen, bathrooms, patio and dining room table) and the microwave. Optionally (I added a manual transfer) the bedroom outlets and Fridge (same circuit) Original plan was to power fridge on electricity when driving ... Did nto work.. Powers fan while sleeping and charges phone though .


Home is where I park it.
Kenwood TS-2000 housed in a 2005 Damon Intruder 377


enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 10/10/19 07:14am Link  |  Quote  |  Print  |  Notify Moderator

Grounds can be on a shared buss. Neutrals must be on a separate buss.
Your idea is a very bad idea! Your output from the inverter should be in a separate sub-panel. Leave the 50 amp shore power as is. Second leg normally powers other systems such as water heater, washer/dryer, or second AC unit.


Bud
USAF Retired
Pace Arrow

2003 Chev Ice Road Tracker


joe6789

TX

New Member

Joined: 10/10/2019

View Profile


Offline
Posted: 10/10/19 08:42am Link  |  Quote  |  Print  |  Notify Moderator

larry cad wrote:

All the grounds tie together. Keep in mind that a 2000 watt inverter can only supply about 15-16 amps. A #14 wire can carry that much so your concerns about overloading a neutral are unfounded. However, feeding half of your breaker panel is not necessarily wise. That is why most times the inverter has a separate feed from a 20 amp breaker in the panel, and the output from the inverter is fed to a "sub" panel. Keep in mind that your original panel is also a "sub" panel, meaning the ground and neutral are NOT bonded together in your panel because the ONLY permitted bond occurs at the campground service panel. Hope this helps.


Larry, yes, the neutral and ground bars are not currently bonded and they will stay that way. Regarding the current level, there could potentially be more than the 15-16 amps -- when NOT inverting (when connected to shore power) the current still passes through the inverter to get to the breaker panel, and that could theoretically be up to 50 amps.

Why is feeding half the breaker panel not wise? The method is described by Jack Mayer in the "Splitting" a 50-ampere Load Center here: http://www.jackdanmayer.com/Wiring.html . He warns against it if the inverter only has a 30 amp transfer switch, but my Victron MultiPlus has a 50 amp switch so that's not a concern.

joe6789

TX

New Member

Joined: 10/10/2019

View Profile


Offline
Posted: 10/10/19 08:50am Link  |  Quote  |  Print  |  Notify Moderator

enblethen wrote:

Grounds can be on a shared buss. Neutrals must be on a separate buss.
Your idea is a very bad idea! Your output from the inverter should be in a separate sub-panel. Leave the 50 amp shore power as is. Second leg normally powers other systems such as water heater, washer/dryer, or second AC unit.


Enblethen, if line 1 and line 2 currently share a neutral bus, why must they be on separate neutral buses after the inverter is installed?

Why do you say splitting the existing panel is a bad idea? It basically creates two breaker panels within the one box. Jack Mayer describes the method here (scroll most of the way down to "Splitting" a 50-ampere Load Center): http://www.jackdanmayer.com/Wiring.html

enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 10/10/19 09:17am Link  |  Quote  |  Print  |  Notify Moderator

The neutrals would be from different power sources and must be kept separate.
The inverter neutral should (shall) be grounded where the shore power connection cannot be grounded in the rig and must be complete separate.

Ozlander

Rose Hill, Kansas

Senior Member

Joined: 04/23/2003

View Profile


Offline
Posted: 10/10/19 09:30am Link  |  Quote  |  Print  |  Notify Moderator

You could get a 240 vac inverter/charger. Be simpler the wire, no spiting the panel.


Ozlander

06 Yukon XL
2001 Trail-Lite 7253


time2roll

Southern California

Senior Member

Joined: 03/21/2005

View Profile



Good Sam RV Club Member


Posted: 10/10/19 09:58am Link  |  Quote  |  Print  |  Notify Moderator

Multiplus is the Victron that combines power with a limited source to boost as needed right?

I don't see the circumstances in a 50 amp RV where this is a benefit. Are you plugging into 15 amp limited utility power? Are you trying to run a big RV with a single Honda 2200? Need to understand what you are attempting to accomplish.


2001 F150 SuperCrew
2006 Keystone Springdale 249FWBHLS
675w Solar pictures back up

joe6789

TX

New Member

Joined: 10/10/2019

View Profile


Offline
Posted: 10/10/19 11:04am Link  |  Quote  |  Print  |  Notify Moderator

time2roll wrote:

Multiplus is the Victron that combines power with a limited source to boost as needed right?

I don't see the circumstances in a 50 amp RV where this is a benefit. Are you plugging into 15 amp limited utility power? Are you trying to run a big RV with a single Honda 2200? Need to understand what you are attempting to accomplish.


Time2roll, you are correct. The Multiplus can supplement short power with inverted battery power simultaneously. However, I don't expect to need that feature. I will usually either be connected to 50A shore power or boondocking off batteries (with occasional generator use).

I bought the Multiplus because it is a combined inverter plus battery charger, has good quality and reputation, and was recommended for charging lithium batteries (which my existing converter can't do well).

I am looking for the simplest installation. It seems like splitting the existing breaker panel is easier than installing a subpanel, which would require finding a place for a whole new panel and extending a bunch of the circuit wiring. Most of the circuits I want to run off the inverter are already on the same leg in my existing box, so I thought it would be relatively simple to just run the one leg through the inverter and leave the other leg as-is.

But the fact that there's just one shared neutral wire for both hot legs is where I'm not sure what to do.

Thanks for the help!

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 4  
Next

Open Roads Forum  >  Tech Issues

 > Wiring neutral/ground when splitting panel for MultiPlus?
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2019 CWI, Inc. © 2019 Good Sam Enterprises, LLC. All Rights Reserved. | Terms of Use | PRIVACY POLICY | YOUR PRIVACY RIGHTS