Posted: 10/11/19 11:15am Link  |  Quote  |  Print  |  Notify Moderator
The issue with grounds (grounds are grounds) and neutrals (neutrals are neutrals) is to keep them separated to prevent eddy currents between the two, and for the same reason it’s best to tie each into it’s own dedicated buss-bar...
enblethen
Moses Lake, WA
Posted: 10/11/19 11:21am Link  |  Quote  |  Print  |  Notify Moderator
neutrals are not always common. It depends on the overall system as whether they can or cannot be tied together.
The block diagram shows separating the neutrals via the relay.
Bud
USAF Retired
Pace Arrow
2003 Chev Ice Road Tracker
3 tons
NV.
Posted: 10/11/19 02:12pm Link  |  Quote  |  Print  |  Notify Moderator
In Appendix B of the manual, it appears to me that the relay is for the purposes of bonding neutral to ground when outside power is not present...This is typical of many inverter-chargers and provided due to NEC code.
https://www.victronenergy.com/upload/documents/Manual-MultiPlus-Compact-2000-120V-EN.pdf
enblethen
Moses Lake, WA
Posted: 10/11/19 02:30pm Link  |  Quote  |  Print  |  Notify Moderator
Appendix B diagram is to ground the neutral as required by the NEC is correct. That changes it from a floating neutral to one that is grounded.
The transfer relay still opens the neutral.
3 tons
NV.
Posted: 10/11/19 03:29pm Link  |  Quote  |  Print  |  Notify Moderator
I’m confused, I see no other relay in the block diagram - what am I missing?
MrWizard
Traveling
Posted: 10/11/19 03:47pm Link  |  Quote  |  Print  |  Notify Moderator
If this has a 50 amp internal RV transfer switch
Just install it correctly
Both sides get either inverter or shore power
your Idea
Only one leg feeding inverter and then one side of breaker panel and one leg direct to panel
Doesn't make sense to me , it might even be against NEC
Unplug shore cord, inverter is on, stick hand in panel get shocked any way
Sounds like trouble too Me
* This post was edited 10/12/19 12:05am by MrWizard *
Radiate The Happy
1997 F53 Bounder 36s
enblethen
Moses Lake, WA
Posted: 10/11/19 04:51pm Link  |  Quote  |  Print  |  Notify Moderator
They call it a "backfeed safety relay".
joe6789
TX
Posted: 10/16/19 11:28am Link  |  Quote  |  Print  |  Notify Moderator
Thanks everyone for your advice. I just heard back from Victron via email. I think I understand their response but it would be helpful if anyone else could confirm I'm interpreting correctly. I had asked them whether the neutral wire needs to be branched, so that line 1 and line 2 have separate neutral wires into the breaker box and potentially even separate neutral bus bars. Sounds like the answer is "No" -- to simply run line 2 direct to the breaker box without its own separate neutral/ground, and then run line 1 through the inverter along with neutral and ground.
Victron's exact response:
For proper current measurement and control, as well a preventing multiple return paths, it is advised to run the ground an N through the Multi without branching off to the L2 line first:
1) Only one side of the distribution panel would be powered by the inverter when not plugged in. Also no 240V inverter loads are possible with just one Multi.
2) If you only have single-phase 120V input available, make sure it is on the L1 line through the Multi. If you try to run it to the L2, the open input relay on the Multi will prevent a complete circuit. You would want it this way for charging anyway.
Does that all make sense? In the image he sent, it looks like the power source is coming from a breaker box on the right rather than a shore power cord, but I assume the answer would be the same in a shore power or generator sourced setup.
The other thing that could be troubling is his point #2. Let's say I'm using a 30A to 50A adapter cord to to plug into 30A shore power or a generator... my understanding is the the adapter provides (a smaller amount of) current into both legs of the 50A cord. So I don't think his point about the open input relay preventing a complete circuit would apply in that case, since both L1 and L2 would be receiving power.
Again, would appreciate if others have comments. This seems to be the simplest possible setup for me. It doesn't require installing a separate breaker box. I'll simply need a little junction box so I can splice and extend the L1, N, & G to the inverter and back.
Thanks,
Joe
enblethen
Moses Lake, WA
Posted: 10/16/19 11:47am Link  |  Quote  |  Print  |  Notify Moderator
The drawing is too vague! Yes, it shows coming from a main disconnect through the inverter to a distribution panel.
I still say the easiest is to run your one branch circuit from the distribution panel and run it to the inverter output. Yes, you would need to run a feed from the distribution panel to the 120 volt input to the inverter.
time2roll
Posted: 10/16/19 04:30pm Link  |  Quote  |  Print  |  Notify Moderator
Yes. This is same as we discussed earlier.
Single phase 120v will feed L1 & L2 and close the relay for normal operation on 30 amp service.