Posted: 11/06/19 08:10am Link  |  Quote  |  Print  |  Notify Moderator

Have a 2003 36' Gulfstream Ultra Supreme. Never had issues with A/C's b4 & don't know anything about them? I do have an issue with the front unit now.Unit works as intended when controlled by thermostat. But, when Off @ thermostat & plugging up 2 shoreline; 50 amp service; &/or running power with 5500 On an generator, as soon as u plug in or generator is initiated..... the front unit Air comes on; thermostat OFF;sounds if it trying to come ON?? Trying, because it's only running w/NO air coming out??? As soon as power to Coach, it runs 4 2 to 3 mins. and off for 20 min then cycles like that throughout having power source?? I checked Converter, it was fine, but upgraded to another that has 3 step charging instead of single phase. I'm cautious of covering back up with this problem. Could u help??

enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 11/06/19 08:56am Link  |  Quote  |  Print  |  Notify Moderator

I would verify that the power to the rig is correct.
Test the system to insure the neutral is in good shape.
One of the small three light tester may aid in this test.
best way is to use a volt meter. test at the 120/240 volt distribution panel.
First item that could be issue is the neutral relay in the transfer sitch.


Bud
USAF Retired
Pace Arrow

2003 Chev Ice Road Tracker


Chris Bryant

Arden, North Carolina

Senior Member

Joined: 03/26/2003

View Profile



Posted: 11/06/19 10:12am Link  |  Quote  |  Print  |  Notify Moderator

Sounds like the compressor relay is welded closed on the upper circuit board. You should shut the breaker to it, as it will run the compressor and cycle on the overload as it overheats.


-- Chris Bryant
My RV Service Blog
The RV.net Blog

crawford

Dandridge Tenn.

Senior Member

Joined: 03/22/2006

View Profile



Good Sam RV Club Member

Offline
Posted: 11/07/19 05:54pm Link  |  Quote  |  Print  |  Notify Moderator

It sounds like your are saying when Genny is ingaged you have a problem if you check you circuit breakers on Gennys itself one my be tripped.


Change from a c class to a A class Georgetown 07 triple slide

BamaUltra

Georgia

New Member

Joined: 11/05/2019

View Profile


Offline
Posted: 11/07/19 06:11pm Link  |  Quote  |  Print  |  Notify Moderator

The a/c works great with either power source? The problem is when unit is in the OFF position and you plug in or crank Genny, the front unit, ONLY; tries to come on for 2 mins. and cycles that way; with NO air coming from vent; off for 20 mins. & Does those cycles as long as power is coming to it? No matter which source? I can go in & operate with thermostat ON & control thru temps & works just fine with air coming from vents & all?

dougrainer

Carrolton, Texas

Senior Member

Joined: 06/11/2007

View Profile


Offline
Posted: 11/07/19 07:21pm Link  |  Quote  |  Print  |  Notify Moderator

AS Chris told you, the Compressor relay is fused closed. The Compressor is coming ON and because NO FAN is running, the compressor is overloading and the Overload switch kicks it out. When it cools down, it comes back on. You need a new upper control board. The compressor relay is not a separate part. Doug

Chris Bryant

Arden, North Carolina

Senior Member

Joined: 03/26/2003

View Profile



Posted: 11/08/19 02:27am Link  |  Quote  |  Print  |  Notify Moderator

BamaUltra wrote:

The a/c works great with either power source? The problem is when unit is in the OFF position and you plug in or crank Genny, the front unit, ONLY; tries to come on for 2 mins. and cycles that way; with NO air coming from vent; off for 20 mins. & Does those cycles as long as power is coming to it? No matter which source? I can go in & operate with thermostat ON & control thru temps & works just fine with air coming from vents & all?


Not sure why every sentence is a question, but I stand by my last post- your upper circuit board has a bad compressor relay and needs to be replaced, from the symptoms you have given.
.??

BamaUltra

Georgia

New Member

Joined: 11/05/2019

View Profile


Offline
Posted: 11/08/19 09:18pm Link  |  Quote  |  Print  |  Notify Moderator

Thanks so much 4 Ur advice Chris. My Coach being '03, will the board I order from eBay work on a 16 yr. Old control board? U seem very knowledgeable about this? Thanks to y'all again

BamaUltra

Georgia

New Member

Joined: 11/05/2019

View Profile


Offline
Posted: 11/08/19 10:46pm Link  |  Quote  |  Print  |  Notify Moderator

One other thing Chris, if the relay is welded close; shouldn't my AC NOT Work when I control it with thermostat? Cause I can turn it on @ thermostat and set temperature & it cuts On & OFF perfectly? Looks like, to me, it would have same results of relay on board was bad and wouldn't blow air? Just saying, I don't know anything about these things. I appreciate all ur advice. Thanks

dougrainer

Carrolton, Texas

Senior Member

Joined: 06/11/2007

View Profile


Offline
Posted: 11/09/19 07:53am Link  |  Quote  |  Print  |  Notify Moderator

There is a Compressor and there is a FAN. Now, When the FAN shuts off from the tstat, the compressor should stay ON if the relay is defective. If both the FAN and Compressor shut OFF when the tstat temp is reached, you relay is working. One thing you can do, is swap the front and rear control boards. If the problem follows the control board you have a defective control board. Are you POSITIVE that when operated by the tstat and the system shuts OFF, that the compressor does not come on in the next 10 to 20 minutes by itself? Doug

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 2  
Next

Open Roads Forum  >  Class A Motorhomes  >  General Topics

 > A/C ghosts??
Search:   Advanced Search

Search only in Class A Motorhomes


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2019 CWI, Inc. © 2019 Good Sam Enterprises, LLC. All Rights Reserved. | Terms of Use | PRIVACY POLICY | YOUR PRIVACY RIGHTS