Posted: 01/11/20 10:01pm Link  |  Quote  |  Print  |  Notify Moderator

As posters asked:

Always at same park (and pedestal)?

Happening at many different campgrounds? - (etc.)

Help out to determine if it's your problem - or theirs!

The 30amp pedestal connection is the most frequently used at parks, and often is not regularly replaced. The slots get "sloppy" and loose from usage over time. (often *years* of use!)

An easy solution is to use the 50amp pedestal outlet (assuming the pedestal has one) with a 50 to 30 amp adapter for a better connection.

.

Janss

Sedona, AZ

Senior Member

Joined: 04/29/2010

View Profile



Good Sam RV Club Member

Offline
Posted: 01/11/20 10:08pm Link  |  Quote  |  Print  |  Notify Moderator

I had my plug melt once. Turned out that the cord connection at the other end, IN my motorhome was loose. There were 2 loose screws causing the wires to not make solid connections. Causes a lot of heat. I noticed my whole cord was quite warm too.


2002 Itasca Suncruiser 32V
2012 Suzuki Grand Vitara

Dave H M

IL

Senior Member

Joined: 08/11/2006

View Profile


Offline
Posted: 01/12/20 06:23am Link  |  Quote  |  Print  |  Notify Moderator

Dustin, are you referring to the same RV park plug or is this happening at more than one park?

Old-Biscuit

Verde Valley

Senior Member

Joined: 06/20/2009

View Profile



Posted: 01/12/20 09:06am Link  |  Quote  |  Print  |  Notify Moderator

WOW......three times melted plug

Problem is NOT at the power pedestal it is in your power cord OR Main Power Panel

Need to go thru the wire connections in Main Panel and TIGHTEN them UP
Might even find 'evidence' of overheating at connections

Hot wire to Main CB (Black)
Ground wire to terminal strip (Green)
NEUTRAL wire connedction (which is most likely loose) (White)


Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
On the Road Debt Free April '07
Off the road still Debt Free Jan. '14

ksg5000

Oregon

Senior Member

Joined: 06/30/2008

View Profile



Posted: 01/12/20 10:01am Link  |  Quote  |  Print  |  Notify Moderator

Also - when you replace the plug are you making sure you cut back the wire so that you eliminate any of the damaged/brittle wire?


Kevin

enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile






Posted: 01/12/20 10:06am Link  |  Quote  |  Print  |  Notify Moderator

Not only cut back wire, but apply good coating of de-oxidation compound on wire connection points.


Bud
USAF Retired
Pace Arrow

2003 Chev Ice Road Tracker


MNRon

Tennessee

Senior Member

Joined: 08/18/2007

View Profile



Good Sam RV Club Member

Offline
Posted: 01/12/20 06:20pm Link  |  Quote  |  Print  |  Notify Moderator

Question for those wiser than me: If plug is melting (I assume he means one of the electrodes in the plug) that is evidence of too much heat at that point. That heat is caused by current and resistance, right?

IF the electrode has a solid connection into the socket why would a loose connection downstream cause that contact point to overheat? A short downstream would trip a breaker before current got crazy. A loose connection could cause lots of current spikes, potentially too short to trip a breaker, but I would expect the arcing (and associated heating/melting) to be at the point of the loose connection. If the plug electrode were solidly connected to the receptacle I wouldn’t think it would be a point of excessive heating.

With all that said, a plug connection will have some resistance but I would expect that to be much smaller than the resistance of the downstream intermittent connection. So again that is where I would expect arcing and melting.

Long way to say I think that if he’s having melting of his plug electrode, I would be looking for reasons it wasn’t making a solid connection and result in arcing there, not be looking first for downstream issues.

What am I missing?


Ron & Pat
2013 Silverado 3500 Duramax SRW
2019 VanLeigh Vilano 320 GK

Lynnmor

Red Lion

Senior Member

Joined: 07/16/2011

View Profile



Good Sam RV Club Member


Posted: 01/13/20 01:56am Link  |  Quote  |  Print  |  Notify Moderator

Flute Man wrote:

Sounds like the park needs to replace or repair the socket in their pedestal. Poor connections cause heat.


This is the correct answer and it was the very first reply.





larry cad

ohio

Senior Member

Joined: 05/23/2004

View Profile





Offline
Posted: 01/13/20 04:22am Link  |  Quote  |  Print  |  Notify Moderator

MNRon wrote:

Question for those wiser than me: If plug is melting (I assume he means one of the electrodes in the plug) that is evidence of too much heat at that point. That heat is caused by current and resistance, right?

IF the electrode has a solid connection into the socket why would a loose connection downstream cause that contact point to overheat? A short downstream would trip a breaker before current got crazy. A loose connection could cause lots of current spikes, potentially too short to trip a breaker, but I would expect the arcing (and associated heating/melting) to be at the point of the loose connection. If the plug electrode were solidly connected to the receptacle I wouldn’t think it would be a point of excessive heating.

With all that said, a plug connection will have some resistance but I would expect that to be much smaller than the resistance of the downstream intermittent connection. So again that is where I would expect arcing and melting.

Long way to say I think that if he’s having melting of his plug electrode, I would be looking for reasons it wasn’t making a solid connection and result in arcing there, not be looking first for downstream issues.

What am I missing?


Thank you. This is so obvious I was wondering if it was worth stating and you beat me to it. Some of the previous suggestions were so far out I am amazed! And yes, I agree the problem is at the plug and CG receptacle, not in the OP breaker panel, etc. Hopefully the OP can discern the wheat from the chaff.


Today is my personal best for most consecutive days alive.

Our Travel Blog

Campinghoss@51

Windsor NC

Senior Member

Joined: 11/03/2003

View Profile



Good Sam RV Club Member

Offline
Posted: 01/13/20 04:25am Link  |  Quote  |  Print  |  Notify Moderator

Yep, the problem is in the cg's receptacle. If the contacts in the receptacle are not making good contact on both sides of each of the male prongs it is generating heat and will cause the problem. Sometimes folks will tell you to bend the male prongs out so it will fit tighter in the receptacle. That is totaling incorrect and will just compound the problem.


Camping Hoss
2017 Open Range 3X 388RKS
2017 F-350 6.7 with hips 8'bed
Lucky & Lucie


Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 4  
Prev  |  Next

Open Roads Forum  >  Fifth-Wheels

 > melting plug
Search:   Advanced Search

Search only in Fifth-Wheels


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.