 > Low Voltage on One 50A Leg

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 3  
Prev  |  Next
Sponsored By:
Bumpyroad

Virginia

Senior Member

Joined: 12/01/2005

View Profile


Offline
Posted: 07/31/20 04:20pm Link  |  Quote  |  Print  |  Notify Moderator

camperdave wrote:

so as a 30a RVer, sounds like it may be worth carrying two 50a - 30a adapters, one for each line. Pick the one with the higher voltage. Anyone do that instead of plugging into the 30a receptacle?


at one time I was going to take my continuity tester to the RV stores and test the 30/50 amp pigtails to see if I could find two that were different but thought better of it. [emoticon]
you could of course make your own adapter.
bumpy





pianotuna

Regina, SK, Canada

Senior Member

Joined: 12/18/2004

View Profile


Offline
Posted: 07/31/20 04:39pm Link  |  Quote  |  Print  |  Notify Moderator

Camperdave,

You would have to "roll your own". If going that far--why not build a "break out box" so you could have twin 30 amp outlets, one for each "leg". I added breakers to my "box" as well.

* This post was edited 07/31/20 05:35pm by pianotuna *


Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp hours of AGM in two battery banks 12 volt batteries, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 07/31/20 04:51pm Link  |  Quote  |  Print  |  Notify Moderator

Generally this idicates a weak Neutral but it can happen that almost all the park is on one leg (the low one) YOu need multiple voltage meausurements
The Park outlet (Sadly it's hard to measure when plugged in but if the box has 20-3--50 measure the 20 and 30 (use a puck style adapter on the 30 and a plug in meter) as these are usually on different legs (not always)

The park distribution box is also a test point but .... for the park not you.


Home is where I park it.
Kenwood TS-2000 housed in a 2005 Damon Intruder 377


CA Traveler

The Western States

Senior Member

Joined: 01/03/2004

View Profile


Offline
Posted: 07/31/20 04:52pm Link  |  Quote  |  Print  |  Notify Moderator

camperdave wrote:

so as a 30a RVer, sounds like it may be worth carrying two 50a - 30a adapters, one for each line. Pick the one with the higher voltage. Anyone do that instead of plugging into the 30a receptacle?
It's common practice to use a 50/30 adapter for 30A RVs for better voltage.

However voltage continues to vary and a autoformer would be a better option.


2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob


DrewE

Vermont

Senior Member

Joined: 08/23/2014

View Profile


Offline
Posted: 07/31/20 06:56pm Link  |  Quote  |  Print  |  Notify Moderator

Gdetrailer wrote:


I suspect what the OP is seeing is an issue in the campgrounds electrical system coming from MORE 30A 120V usage..

Most pedestals will by default have the 30A 120V outlet on the SAME "Line" and most likely that default IS L1, and more folks will be hooked up to the 30A outlets..

Hence the reason OP is seeing the voltage mismatch..


Given that the pedestals would presumably all be wired identically, it would be very odd for a campground not to wire up half the pedestals in the loop with the two legs swapped from the other half of the pedestals, such that the 30A sockets would tend to balance each other out. There's nothing other than an arbitrarily chosen convention that makes one particular leg L1 rather than L0, after all.





Roger10378

Goodrich, MI.

Senior Member

Joined: 05/29/2008

View Profile



Good Sam RV Club Member

Offline
Posted: 07/31/20 07:12pm Link  |  Quote  |  Print  |  Notify Moderator

OP states "in several campgrounds" so that makes it most likely the problem is in his unit. The fact that the higher number is close to nominal says there is something wrong on the side with the low number. I would be looking for a loose connection somewhere in the positive side.


2005 Cardinal 30TS
2007 Chevy 2500HD D/A

beemerphile1

Ohio

Senior Member

Joined: 04/20/2007

View Profile





Offline
Posted: 07/31/20 07:19pm Link  |  Quote  |  Print  |  Notify Moderator

Test your unit. Use an adapter to connect to a 30a service. Voltage on L1 and L2 should be identical, is it? If not, your unit might be adjustable.


Build a life you don't need a vacation from.

2016 Silverado 3500HD DRW D/A 4x4
2018 Keystone Cougar 26RBS
2006 Weekend Warrior FK1900


Acampingwewillgo

USA

Senior Member

Joined: 11/15/2002

View Profile



Good Sam RV Club Member

Offline
Posted: 07/31/20 09:00pm Link  |  Quote  |  Print  |  Notify Moderator

Since I've had erratic measurements a time of two, check both ends of your cord set ....mine had a loose neutral connection on my female Marinco 50 amp plug. A loose connection which soon turned into a burnt connection resulting in no power to RV. A quick trip to pick up a new female and all was well with the world.


96 Vogue Prima Vista
The Kid's: Humphrie, the Mini Schnauzer and Georgie,wire haired dachshund.
Rainbow Bridge: Laddie,Scoutie,Katie,Cooper,Kodie,Rubie,Maggie, Cassie, Mollie, Elvis, Potter and Rosie Love You! (40+ years in all)

Bumpyroad

Virginia

Senior Member

Joined: 12/01/2005

View Profile


Offline
Posted: 08/01/20 07:02am Link  |  Quote  |  Print  |  Notify Moderator

Acampingwewillgo wrote:

. A quick trip to pick up a new female and all was well with the world.


sounds about right.
bumpy

joelc

Cedar Point, NC

Senior Member

Joined: 02/23/2004

View Profile


Offline
Posted: 08/01/20 09:12am Link  |  Quote  |  Print  |  Notify Moderator

Are you reading this at the post or do you have a built in voltage EMS inside your coach? As noted above you need the raw voltage without load. A few volts difference will not matter.

Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
Page of 3  
Prev  |  Next

Open Roads Forum  >  Tech Issues

 > Low Voltage on One 50A Leg
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:




© 2020 CWI, Inc. © 2020 Good Sam Enterprises, LLC. All Rights Reserved.