There is no power reaching the motorhome from the generator.
I tested the leads to the breaker. One read about 170VAC with generator running. I shut the generator off and tested the other lead and it tested .266 kilohms so I don't think there is a short but I'm not very electrically literate.
I replaced the switch. That didn't fix.
AC voltage works fine when I plug into shore power.
I'm wondering what next to check.
Thanks.
1995 Lazy Daze 23.5' TK
Wherever I happen to park
There are shorts you can't find with a VOM. They are voltage dependent.
Alas I can not list them all but I can tell you now to narrow the search
INSIDE the RV turn off EVERY breaker. not fire up the generator. Turn on just the MAIN breaker... Still good (hook a test light or volt meter to the main braker and white bus to check or have partner watch generator breaker)
Ok turn on the next breaker, and the next and the next till CLICK.
Home is where I park it.
Dutch_12078
Winters south, summers north
You might find some help here:
Onan RV Troubleshooting Guide
Dutch
2001 GBM Landau 34' Class A
dougrainer
Carrolton, Texas
The MAX genset voltage is 132 volts. The Voltage range on a Onan is 126 to 132 volts. IF you read 170, why would you think that is OK? THAT either means your Onan voltage regulator is toast or the Genset SPEED is NOT 1800 RPM's at 60 htz. Increase in speed will cause an increase in output voltage. Most common cause of this is novices that increase the idle speed to stop a surge/hunt genset run. This does NOT fix the problem but does stop the Hunt/surge. But does increase the output voltage. Doug
SHRED
With every breaker off on the converter the genset breaker trips off still after about an 8 second delay.
edited 02/18/21 10:31am by SHRED *
time2roll
170v sounds like a regulator issue or an open neutral. Best to have a pro look at this issue.
675w Solar pictures back up
SHRED
time2roll wrote: 170v sounds like a regulator issue or an open neutral. Best to have a pro look at this issue.
I'm in Encinitas, CA (San Diego County).
Do you know of any good shops in my area?
KMLsquared
Cotati CA
While I agree 170VAC is too high, I don't see why that would be tripping a over current device like a breaker. If all down stream loads are off and its tripping there must be a short between that generator breaker and the main breaker of the 120VAC distribution panel. Start tracing wires and opening junction boxes.
Odd the 170V as that is the peak voltage of 120VAC. Is your meter a good one or a cheap harbor freight one?
2002 Doge RAM LB QC 4x4 HO 6spd
2003 Rampage 33TB
2007 CRF80F
2006 TTR50E
2004 CRF70
2002 TTR125L
2002 Banshee
1969 Baja Bug
SHRED
KMLsquared wrote: While I agree 170VAC is too high, I don't see why that would be tripping a over current device like a breaker. If all down stream loads are off and its tripping there must be a short between that generator breaker and the main breaker of the 120VAC distribution panel. Start tracing wires and opening junction boxes.
This is my meter.
It's been very accurate for other applications.
METER
ndrorder
Southwest
170VAC is too high. Disconnect the output wires from the generator breaker to get a good measurement of the voltage between the common and neutral connections at the breaker while the generator is running. If this is more than 132 VAC, generator issues need to be resolved before continuing.
The next step is to isolate the wire past the generator. So with the generator off, leave the output wires from the breaker disconnected and disconnect the generator input wires at the automatic transfer switch (ATS), or unplug the shore power from the generator receptacle. Now measure resistance between the common and neutral wires and common and ground wires. If anything other than an open circuit is measured, there is a short in the wire between the generator and ATS or receptacle that needs to be corrected. Best guess is, because of age, there is a generator receptacle and something inside that box has giggled loose and is shorting.
__________________________________________________
Cliff
2011 Four Winds Chateau 23U