RV.Net Open Roads Forum: Tech Issues: Converter replacement
 > Converter replacement
CA Traveler
The Western States
Posted: 03/16/21 10:25am Link  |  Quote  |  Print  |  Notify Moderator
Specs don't necessarily reflect normal operation. Could be for fuses, heavy load startup, low AC voltage, temperature, power factor, etc.
60A*14.8V*1.2 (20% loss) = 1065W/120V = 9A or about half the gen rating.
Plus how often/long will it actually be charging at that rate?
2014 Grand Cherokee Overland
Bob
BFL13
Victoria, BC
Posted: 03/16/21 10:27am Link  |  Quote  |  Print  |  Notify Moderator
A single 27 will accept about 45 amps at 50% SOC and taper almost right away for its Absorption Stage. If you hit it with 60 amps all that happens is the amps will immediately drop to whatever the 27 will accept and taper from there.
That's with a flooded battery--don't do that with AGM or Si02--stick with their 27% charging limits--ie 27 amps on a 100AH batt or you can use your 55 amper on a pair of 100s. LFP can take it though.
ISTR a Honda 2000 spec is 13.3 amps at 120v for running output of 1600w (VA really)
I prefer the PowerMax line (same as Boondocker, a rebadged PowerMax) but the PD with Charge Wizard might be easier to operate if you are not ready to do manual voltage adjustments to suit your battery specs. (or you can chose the standard three-stage automatic mode if on shore power) If you are on shore power it doesn't matter about which converters--they all do about the same Float voltage.
Most converters at 75 amps and below are not power-factor corrected and their PFs are about 0.7, so you have to add that to what the generator will have to supply.
EG, as measured with a Trimetric and a Kill-A-Watt here is how it works for a 55 amp converter with battery accepting 56.8 amps and rising through 13.7 volts. (3000w Honda generator)
124.7 v, 11.06 a, 980w, 0.7PF, 1380VA (Kill-A-Watt )
So the Honda 1600 VA would supply that 1380VA. Same deal with a 75 amp converter needs the gen supplying 1700 VA, so the Honda 2000 would be a little overloaded. The Honda 2200 is rated for 1800VA though, so that would be ok with a 75 amper.
My B&S P2200 just barely runs my 75 amp converter which pulls 1700VA and the gen is rated at 1700VA.
You have a choice if the WFCO does run of leaving it in place and get a deck mount converter to work with the gen, or else replace the WFCO "lower portion" with a better converter.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
pinesman
virginia
Posted: 03/16/21 10:41am Link  |  Quote  |  Print  |  Notify Moderator
Keep in mind that while your might not generator will not get above idle with the WFCO, putting in one of these better converters will cause your generator to speed up a little for a while, or at least that is my case with my Boondocker 55, 4 batteries and 2000w generator.
pulpwood007
Hemphill, TX
Posted: 03/16/21 11:07am Link  |  Quote  |  Print  |  Notify Moderator
Thanks, good info. This will be a deck mounted (stand alone) converter, not one housed in the power distribution box.
It sounds like the 45 amp converter would be fine for my group 27 lead acid battery, and run well on the EU2000. The only catch is that the 55 amp model is the same price on Amazon.
So. I guess the question is if the single 27 accepts max 45 amps at 50% charge level, will the converter charge output drop accordingly, and hence draw less current on the AC input side? I would think definitely yes since the DC output load has decreased, and I could probably calculate that using the power factor.
Obviously I'd like to go with the 55 amp model which I know the EU2000 would supply, but also have a little power left over to run lights and maybe TV in the trailer. Looks like I need to get the AmpClamp out and do a little measuring.
As far a manual adjustments, I have no problem with that. 99.9% of the time the 3 stage auto mode will be fine. I just want to have the option of locking in boost mode for rapid battery recharge when needed. I do like the remote pendant the PD offers, but again going into the PowerMax as seldom as I would be needing boost would be no issue.
Edit: Just spoke with PowerMax and found the 55 amp converter will draw 975 watts (under full load) from the generator. Looks like I'm golden!
* This post was edited 03/16/21 11:21am by pulpwood007 *
morley
British Columbia
Posted: 03/16/21 11:09am Link  |  Quote  |  Print  |  Notify Moderator
klutchdust wrote:
Best Converter without a doubt. Plug and play, excellent customer service . Call them, tell them what you need. fixed my issues with my batteries boiling in my Class C.
Totally agree Best Converter is the way to go, very simple lower portion replacement of your WFCO. Did it myself and it works well. Randy at Best is the “Best” very helpful and will answer all of your questions if you have any. No more boiled batteries for me now also.
2008 Topaz F254SS 26 ft.
2009 Chevy Silverado, 2500HD, Duramax, Allison Tranny, 4x4, EC
250 watt solar panel system, BlueSky controller and remote
pulpwood007
Hemphill, TX
Posted: 03/16/21 11:23am Link  |  Quote  |  Print  |  Notify Moderator
I've done business with Randy before. Agree, good guy. I can just save a few bucks on the same converter branded as PowerMax.
time2roll
Posted: 03/16/21 11:36am Link  |  Quote  |  Print  |  Notify Moderator
The only trouble with PowerMax is the short absorption time. With 55+ amps the converter will hit the 14.6 volts fairly quick and then you get maybe 15 to 30 minutes at that voltage and you are only about 80% charged when the voltage drops to 13.6.
For a single battery deck mount I recommend the BD 1235CL at just 35 amps. This will get you closer to 90+% charged before the voltage drops. Or go with the PD9245 or PD9260 that will hold the boost voltage a full 4 hours.
675w Solar pictures back up
pulpwood007
Hemphill, TX
Posted: 03/16/21 11:48am Link  |  Quote  |  Print  |  Notify Moderator
I don't think so. PowerMax specs show a switch that can change from three stage auto to manual, locking output at 14.6. One only needs to remember to switch back to auto after fast charging of battery. I do like the remote pendant on the PD. Just wouldn't use it much for the price difference.
PM on auto:14.6 vdc for 0.5 hrs, 13.6 for 12 hrs, then to 13.2.
time2roll
Posted: 03/16/21 12:16pm Link  |  Quote  |  Print  |  Notify Moderator
Yes if you want to adjust the PM manually you are good to go. Sometimes hard to know the technical level of these requests.
BFL13
Victoria, BC
Posted: 03/16/21 12:34pm Link  |  Quote  |  Print  |  Notify Moderator
I didn't check amazon etc but this is a good deal and shipping
https://www.boatandrvaccessories.com/pro........-amp-12-volt-power-supply-with-led-light
As mentioned, your battery will only accept the amps it can at that SOC and at that voltage, so yes get the 55 or even the 60 in case you get a second battery someday.
You need a flashlight and a small screwdriver to do the adjusments, and a voltmeter to watch while you twiddle the pot. You can use cut off ends of jumper cables (#8 or fatter gauge) in the terminals to make it a portable charger.
Looks like they forgot about the PF when telling you the watts---see my post above for the real draw on the gen with a 55 amper (it was with a PowerMax)
They get the 120v input right in their table at 11 amps.
11 x 120v = 1320
EDIT-- note 975 x 100/70 = 1393 which is closer to the 1380 I get.
https://powermaxconverters.com/wp-content/uploads/2019/02/PM3-Spec-Sheet.pdf
* This post was last edited 03/16/21 12:59pm by BFL13 *   View edit history