Posted: 08/11/21 12:10pm Link  |  Quote  |  Print  |  Notify Moderator

Ed_Gee wrote:

To repeat some info - the frequency error occurred at three different RV Parks... all in the eastern Oregon area... I have yet to determine if my DVM measures Frequency.... but I must consider the EMS may have a problem.


I would concur that your EMS is most likely at fault if it is failing on frequency on shore power from the PoCo.

If EMS is faulting over a less than +(-) 2Hz change from PoCo then it must be the EMS.

If it was faulting from your gen only then the issue most likely would be coming from the gen in the form of gen over or under RPM.

EMS systems do fail.. Sometimes they get fussy.

Heck I have a UPS unit that gets bent out of shape when running from my genny and the genny is under light load and constantly switches between UPS battery and shore power unless I add a couple of amps of load to the gen to drop the frequency slightly.. UPS units must synchronize between the shore power and the inverter in order to switch to battery or from battery so they are sometimes persnickety on frequency.

RKW

Four Corners, New Mexico

Senior Member

Joined: 06/07/2002

View Profile



Good Sam RV Club Member

Offline
Posted: 08/11/21 05:43pm Link  |  Quote  |  Print  |  Notify Moderator

For any interconnection (Western Grid, Eastern Grid, ERCOT Grid etc.) the frequency is global. That is to say the frequency is the same throughout each interconnection. In the Western Grid, for example, a control center in New Mexico will read the same frequency as a control center in Washington State. There are no low frequency areas or high frequency areas within an interconnection. If there is a system disturbance, like a sudden loss of load or generation, there will be what is called a frequency excursion. Rarely, if ever, will the excursion be severe enough to cause damage to the customer's equipment. The tripping and separation schemes in an interconnection won't allow it.

So I said all that to explain my observation that the frequency parameter in an EMS is mostly superfluous. The frequency will either be acceptable or it will be zero. The power is either there with an acceptable frequency or it's not there and you are in the dark. I realize this post doesn't answer any thing in the OP, but I wanted to throw it out there for the edification of our forum members.

* This post was last edited 08/11/21 06:15pm by RKW *   View edit history


Ryan

  • 2015 Ford F250
  • 2015 Rockwood Signature Ultralite 8280 WS
  • Dual Honda EU2000i Generators


    The wages of sin are death; but after they're done taking out taxes, it's just a tired feeling.


  • NRALIFR

    Truck Camping Out West

    Senior Member

    Joined: 11/27/2005

    View Profile



    Posted: 08/11/21 05:57pm Link  |  Quote  |  Print  |  Notify Moderator

    [image]

    [emoticon][emoticon]

    wa8yxm

    Davison Michigan (East of Flint)

    Senior Member

    Joined: 07/04/2006

    View Profile


    Offline
    Posted: 08/12/21 05:19am Link  |  Quote  |  Print  |  Notify Moderator

    Ed_Gee wrote:

    NRALIFR - the error code was E7 ... high frequency. Not sure if my DVM will measure frequency.... will check and then keep this in mind...


    Some will. some won't and the Kill-A-Watt meter is what about 30 bucks, it's about a kilo-buck worth of meters in one box
    Voltage
    Frequency
    Volt-amps
    Watts (NOTE these last two are not the same thing)
    Power factor (That's the relationship between watts and V-A)
    Kilowatt hours
    And I think one more (not sure without going to kitchen

    I mentioned power line noise up thread. the PI unit might be more or less senistive to power line noise than either the Kill-a-watt or a DVM with the ability to measure frequency (I have some that do and some that don't by the way)

    A 'scope is the only real way to be sure when you get multiple devices giving different info

    Of course the final option is bad Surge Guard. but not ready for that yet.


    Home was where I park it. but alas the.
    2005 Damon Intruder 377 Alas declared a total loss
    after a semi "nicked" it. Still have the radios
    Kenwood TS-2000, ICOM ID-5100, ID-51A+2, ID-880 REF030C most times


    ktmrfs

    Portland, Oregon

    Senior Member

    Joined: 06/22/2005

    View Profile


    Offline
    Posted: 08/12/21 07:34pm Link  |  Quote  |  Print  |  Notify Moderator

    the only time I would expect the EMS to find a frequency out of range is when connected to an open frame 3600rpm generator that is running at the incorrect rpm. (3600 rpm= 60hz).

    Frequency of the normal "line" coming in is very tightly controlled, seldom will you see even a 1Hz error and the total error in cycles over 24hrs is in the handful. for the grid to work everyone in the grid (3 in the country, east, west, and texas) must be exactly at the same frequency.

    so, If you were connected to campground power and the grid, I suspect the EMS has a fault. BTW on my PD EMS unit that is installed in the trailer I can bypass it with the switch on the "dongle" unit. Nice when using a generator with an unbonded neutral.


    2011 Keystone Outback 295RE
    2004 14' bikehauler with full living quarters
    2015.5 Denali 4x4 CC/SB Duramax/Allison
    2004.5 Silverado 4x4 CC/SB Duramax/Allison passed on to our Son!


    ktmrfs

    Portland, Oregon

    Senior Member

    Joined: 06/22/2005

    View Profile


    Offline
    Posted: 08/12/21 07:35pm Link  |  Quote  |  Print  |  Notify Moderator

    the only time I would expect the EMS to find a frequency out of range is when connected to an open frame 3600rpm generator that is running at the incorrect rpm. (3600 rpm= 60hz).

    Frequency of the normal "line" coming in is very tightly controlled, seldom will you see even a 1Hz error and the total error in cycles over 24hrs is in the handful. for the grid to work everyone in the grid (3 in the country, east, west, and texas) must be exactly at the same frequency and exactly in phase.

    so, If you were connected to campground power and the grid, I suspect the EMS has a fault. BTW on my PD EMS unit that is installed in the trailer I can bypass it with the switch on the "dongle" unit. Nice when using a generator with an unbonded neutral.

    Bobbo

    Wherever I park

    Senior Member

    Joined: 09/16/2007

    View Profile



    Good Sam RV Club Member

    Offline
    Posted: 08/12/21 07:56pm Link  |  Quote  |  Print  |  Notify Moderator

    ktmrfs wrote:

    BTW on my PD EMS unit that is installed in the trailer I can bypass it with the switch on the "dongle" unit. Nice when using a generator with an unbonded neutral.

    My bonding plug (less than $2 to make) means I don't have to bypass the EMS. It protects against generator failure too.


    Bobbo and Lin
    2017 F-150 XLT 4x4 SuperCab w/Max Tow Package 3.5l EcoBoost V6
    2017 Airstream Flying Cloud 23FB


    ktmrfs

    Portland, Oregon

    Senior Member

    Joined: 06/22/2005

    View Profile


    Offline
    Posted: 08/13/21 08:51am Link  |  Quote  |  Print  |  Notify Moderator

    Bobbo wrote:

    ktmrfs wrote:

    BTW on my PD EMS unit that is installed in the trailer I can bypass it with the switch on the "dongle" unit. Nice when using a generator with an unbonded neutral.

    My bonding plug (less than $2 to make) means I don't have to bypass the EMS. It protects against generator failure too.


    I generally also use a bonding plug but on occasion have misplaced it so being able to bypass the EMS has been helpful.

    Reply to Topic  |  Subscribe  |  Print Topic  |  Post New Topic  | 
    Page of 2  
    Prev

    Open Roads Forum  >  Tech Issues

     > Progressive Industries EMS and Powerline frequency error
    Search:   Advanced Search

    Search only in Tech Issues


    New posts No new posts
    Closed, new posts Closed, no new posts
    Moved, new posts Moved, no new posts

    Adjust text size:




    © 2021 CWI, Inc. © 2021 Good Sam Enterprises, LLC. All Rights Reserved.