Janss
Sedona, AZ
We were parked at a casino overnight. Generator and electricity worked fine in the evening. Next morning, electricity stopped midstream as the coffee was filling the cup. But generator was still running. Shore power works, as our next several days were in RV parks.
No circuit breakers appeared to have flipped off, but after this happened, I purposely flipped them all off and then on again....on the generator and every breaker inside the coach. Aux batteries are good. One had a slightly loose negative cable. Tightened that, but still didn't fix the problem.
This coach has an automatic transfer switch box in the electric storage bay. Didn't see anything loose in there. Nothing felt hot.
Any ideas?
2002 Itasca Suncruiser 32V
2012 Suzuki Grand Vitara
CA Traveler
The Western States
CBs can be deceptive - push them fully off then on. Check inverter CBs also as some pass through 120V.
Next I would unplug shore power and measure AC in and out of transfer switch with the gen running to isolate the problem. BUT don't do this unless you fully understand the danger involved and related safety.
2014 Grand Cherokee Overland
Bob
CA Traveler
The Western States
Also a good idea to check, clean and tighten DC and AC connections. RVs vibrate and bounce down the road and connections become loose. Unplug, solar off, gen off, batteries disconnected. Again safety as a battery short can get very hot in an instant.
BB_TX
McKinney, Texas
Generator was running but did you verify it was actually putting out power? Some generators have an overload reset pushbutton that must be pushed in addition to breakers.
wolfe10
Yes, turn OFF and back ON the breakers on the generator itself.
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240
wing_zealot
East of the Mississippi
You need to limit the choices by starting at the source and moving forward. First check if gen is outputting 120 volt, if yes is there 120 incoming from gen at transfer switch, if yes, is there 120 output at transfer switch - and keep going down the line until you isolate the culprit. As it is now, you’re just throwing darts with a blindfold on.
bgum
South Louisiana
You are running what brand name and model genny?
schlep1967
Harrisburg, PA
Did you check the GFI outlet in the kitchen or bathroom?
2008 Dodge Ram 2500 Diesel
2009 Open Range 385RLS
Pull-Rite Super Glide
Janss
Sedona, AZ
Thank you all for your responses.
bgum...Onan 5500 Marquis Gold
schlep1967...Had already pushed GFI several times, black and red, with no clicking. If shore power is powering everything, should I assume no problem with GFI?
wolfe10...I had already done that.
BB TX...I don't see a reset button.
Yes, I totally agree that I need to isolate exactly which step is not putting out power. But I don't know how to do that and realize there is a safety issue. I have a multimeter (which I set on "Volts"), but don't know exactly where to touch the red and black probes. And with or without gennie running? I see on the generator a positive terminal and also the word "ground" on a piece of metal. I had opened the transfer box and touched the probes on screws holding wires in place (without gennie running), but no reading.
I sure don't know much about electricity, so need baby step instructions
bgum
South Louisiana
RESETTING CIRCUIT BREAKERS
If a circuit breaker in the main power distribution
panel of the vehicle or on the genset (Figure 7) trips,
either a circuit shorted or too many appliances were
running. Note that the genset may continue to run
after a circuit breaker trips.
If a circuit breaker trips, disconnect or turn off as
many loads as possible and reset the circuit
breaker. (Push the circuit breaker to OFF to reset it
and then to ON to reconnect the circuit.) If the circuit
breaker trips right away, either the electrical dis-
tribution system has a short circuit or the circuit
breaker is faulty. Call a qualified electrician.
If the circuit breaker does not trip, reconnect the ap-
pliances, one by one, up to a total load that does not
overload the genset or cause the circuit breaker to
trip. If a circuit breaker trips right away when an ap-
pliance is connected, the appliance probably has a
short.
Electrical appliances and tools must be used and
maintained properly and be properly grounded to
cause the line circuit breakers to trip when short cir-
cuits occur.
WARNING Short circuits in electrical
appliances and tools can cause fire and electri-
cal shock leading to severe personal injury or
death. Read and follow the equipment and tool
manufacturer’s instructions and warnings
regarding use, maintenance and proper
grounding.
CONNECTING UTILITY POWER
A vehicle with provisions for connecting utility power
must have an approved device to keep the genset
and utility from being interconnected. See the gen-
set Installation Manual for more information.
WARNING Interconnecting the genset and the
public utility (or any other power source) can
lead to electrocution of utility line workers,
equipment damage and fire. Use an approved
switching device to prevent interconnections.
LINE CIRCUIT
Straight from the manual.
There appears to be two reset switches next to each other on the genny.
edited 10/15/21 07:00pm by bgum *