I need to put a 30 amp 125 volt outlet 250 feet away from main panel I need to know what size wires to get or romex and material needed, outlet is going to be for travel trailer and will be occupied.
* This post was
edited 03/30/23 05:31am by Red man *
|
eHoefler

ozark mountains

Senior Member

Joined: 10/22/2011

View Profile

Offline
|
You need 1/0 aluminum for that distance you would get less than 3% voltage drop
2021 Ram Limited, 3500, Crew Cab, 1075FTPD of Torque!, Max Tow, Long bed, 4 x 4, Dually,
2006 40' Landmark Mt. Rushmore
|
midnightsadie

ohio

Senior Member

Joined: 01/07/2008

View Profile

Offline
|
while your doing this up grade to 50amp during the summer you might need two ac units.or upgrade your rv in the future,
|
valhalla360

No paticular place.

Senior Member

Joined: 08/19/2009

View Profile


Good Sam RV Club Member
|
Consider running it in a PVC conduit so you can easily run new or different cables in the future
Tammy & Mike
Ford F250 V10
2021 Gray Wolf
Gemini Catamaran 34'
Full Time spliting time between boat and RV
|
rhagfo

Portland, OR

Senior Member

Joined: 07/06/2012

View Profile


Good Sam RV Club Member
Offline
|
valhalla360 wrote: Consider running it in a PVC conduit so you can easily run new or different cables in the future
This^^^^
Make sure the conduit is large enough to carry wires large enough for a 50 amp service.
Russ & Paula the Beagle Belle.
2016 Ram Laramie 3500 Aisin DRW 4X4 Long bed.
2005 Copper Canyon 293 FWSLS, 32' GVWR 12,360#
"Visit and Enjoy Oregon State Parks"
|
|
wanderingbob

monticeeo, fla

Senior Member

Joined: 07/26/2012

View Profile

Offline
|
# 6 sez google
|
Gary45

Oshawa, Ontario, Canada

Full Member

Joined: 08/14/2020

View Profile

Offline
|
I would find out electrical code in your area for buried wiring.
|
C.B.

APPLETON WI USA

Senior Member

Joined: 12/15/2003

View Profile


Good Sam RV Club Member
Offline
|
valhalla360 wrote: Consider running it in a PVC conduit so you can easily run new or different cables in the future
X2
CBVP2004~FORD~F350~CC~LARIAT~SRW~SB~4X4~6.0D~
AUTO~PULLRITE 16K SUPERGLIDE~DEMCO GLIDERIDE~
PRODIGY CONTROLLER~C-BETR MIRRORS~EMS-HW50C~
Butch/Barb=2013-Cedar Creek 36CKTS
Kris/Katy=2006-Cherokee 32B
|
BB_TX

McKinney, Texas

Senior Member

Joined: 04/04/2005

View Profile

Offline
|
2 gauge as a minimum. And yes to the conduit.
http://wiresizecalculator.net/
|
2oldman

NM

Senior Member

Joined: 04/15/2001

View Profile

Offline
|
Gary45 wrote: I would find out electrical code in your area for buried wiring. Yah, and maybe see if you need a permit.
|
|